Hİ,

How to make tags for ABB PLC in Ignition SCADA?

Is there a video on how to make the settings?

---

<div class="post-metadata">

**Author:** ![dkhayes117](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/dkhayes117/32/68344_2.png) [@dkhayes117](https://forum.inductiveautomation.com/u/dkhayes117)\
**Post date:** [January 8, 2020, 2:48pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/2 "2020-01-08T14:48:55Z")

</div>

If you haven’t checked out [www.inducitveuniversity.com](http://www.inducitveuniversity.com) yet there is a lot of info there. I’ve never used ABB PLCs before, but if it supports Modbus you can use the Modbus driver in the Ignition gateway, gateway-\>configure-\>devices to connect. If not, Kepware has drivers for ABB Totalflow which would work if that is the protocol it uses. The Ignition online manual has pages on Modbus connections and Kepware integration.  
[https://docs.inductiveautomation.com/display/DOC79/Connecting+to+Modbus+Device](https://docs.inductiveautomation.com/display/DOC79/Connecting+to+Modbus+Device)  
[https://docs.inductiveautomation.com/display/DOC79/Connecting+to+Kepware+OPC-UA](https://docs.inductiveautomation.com/display/DOC79/Connecting+to+Kepware+OPC-UA)

---

<div class="post-metadata">

**Author:** ![tamer\_akti\_26](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tamer_akti_26/32/12617_2.png) [@tamer\_akti\_26](https://forum.inductiveautomation.com/u/tamer_akti_26)\
**Post date:** [January 9, 2020, 9:22pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/3 "2020-01-09T21:22:08Z")

</div>

thanks for your answer.

 ![PLC_DATAs](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/864b99faa1640e09647b41165ddf9079638d83d4.png) ![error_1](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/8c06b01520360ce974141c02372648771a032636.png)

I could not define the path to the “OPC item path”.

How do I name it.

---

<div class="post-metadata">

**Author:** ![tamer\_akti\_26](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tamer_akti_26/32/12617_2.png) [@tamer\_akti\_26](https://forum.inductiveautomation.com/u/tamer_akti_26)\
**Post date:** [January 9, 2020, 10:08pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/4 "2020-01-09T22:08:22Z")

</div>

plc device is a connecting one is disconnected. why does this?

 ![disconneted](https://us1.discourse-cdn.com/inductiveautomation/original/2X/4/4db76bea786b946b44762808f8d4f506227c725b.png) ![connected](https://us1.discourse-cdn.com/inductiveautomation/original/2X/4/4ea9d419a6e1412c4a640151fcb36fd96fe6ac84.png)

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [January 9, 2020, 10:35pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/5 "2020-01-09T22:35:06Z")

</div>

What does the “Details” button show?

---

<div class="post-metadata">

**Author:** ![tamer\_akti\_26](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tamer_akti_26/32/12617_2.png) [@tamer\_akti\_26](https://forum.inductiveautomation.com/u/tamer_akti_26)\
**Post date:** [January 9, 2020, 10:41pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/6 "2020-01-09T22:41:33Z")

</div>

detail.

 ![detail_](https://us1.discourse-cdn.com/inductiveautomation/original/2X/2/2d07e244b76c61eb65f7464603046d985e064067.png)

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [January 9, 2020, 10:46pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/7 "2020-01-09T22:46:10Z")

</div>

Change the Min level to “Trace”

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [January 9, 2020, 10:48pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/8 "2020-01-09T22:48:05Z")

</div>

And click the blue “+” to the right of those 4 messages.

---

<div class="post-metadata">

**Author:** ![tamer\_akti\_26](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tamer_akti_26/32/12617_2.png) [@tamer\_akti\_26](https://forum.inductiveautomation.com/u/tamer_akti_26)\
**Post date:** [January 9, 2020, 10:50pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/9 "2020-01-09T22:50:12Z")

</div>

![res11](https://us1.discourse-cdn.com/inductiveautomation/original/2X/0/042257e5ec11fac504ce85698190264076b13d88.png)

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [January 9, 2020, 11:00pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/10 "2020-01-09T23:00:39Z")

</div>

And click the blue “+” to the right of the SocketDelegate error

---

<div class="post-metadata">

**Author:** ![tamer\_akti\_26](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tamer_akti_26/32/12617_2.png) [@tamer\_akti\_26](https://forum.inductiveautomation.com/u/tamer_akti_26)\
**Post date:** [January 9, 2020, 11:02pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/11 "2020-01-09T23:02:19Z")

</div>

![ress22](https://us1.discourse-cdn.com/inductiveautomation/original/2X/7/70df615a4ba1c0c05674c24e1d9d426810543fe5.png)

---

<div class="post-metadata">

**Author:** ![Rv.Batista](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/rv.batista/32/3593_2.png) [@Rv.Batista](https://forum.inductiveautomation.com/u/Rv.Batista)\
**Post date:** [January 10, 2020, 6:39pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/12 "2020-01-10T18:39:37Z")

</div>

You are able to get data but it keeps going to disconnected?

It is an AC500? If so, they have a small default connection timeout OMB Time , already had problem with this with another SCADA system.

---

<div class="post-metadata">

**Author:** ![Rv.Batista](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/rv.batista/32/3593_2.png) [@Rv.Batista](https://forum.inductiveautomation.com/u/Rv.Batista)\
**Post date:** [January 10, 2020, 6:43pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/13 "2020-01-10T18:43:43Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/f/faa3d2aab74849191b7a4f4a5d52e0f8021c8ca1.png) with firmware 2.3.3+

---

<div class="post-metadata">

**Author:** ![tamer\_akti\_26](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tamer_akti_26/32/12617_2.png) [@tamer\_akti\_26](https://forum.inductiveautomation.com/u/tamer_akti_26)\
**Post date:** [January 10, 2020, 8:11pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/14 "2020-01-10T20:11:28Z")

</div>

Is there a setting?  
tag s gives error. When we say reflesh data flows again.

---

<div class="post-metadata">

**Author:** ![Rv.Batista](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/rv.batista/32/3593_2.png) [@Rv.Batista](https://forum.inductiveautomation.com/u/Rv.Batista)\
**Post date:** [January 10, 2020, 8:14pm UTC](https://forum.inductiveautomation.com/t/how-to-make-tags-for-abb-plc-in-ignition-scada/31145/15 "2020-01-10T20:14:21Z")

</div>

Yes, OMB time is a setting under modbus tcp server object. You access it in Automation Builder project tree.