I have a file upload component which when uploads image file save it to database and flex repeater is used to retrieve the uploaded image file from the database and display it, how can I write a script for deleting the particular image from database when I press the delete button in the flex repeater.

Thank You.

---

<div class="post-metadata">

**Author:** ![cmallonee](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/cmallonee/32/6416_2.png) [@cmallonee](https://forum.inductiveautomation.com/u/cmallonee)\
**Post date:** [March 10, 2020, 4:42pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/2 "2020-03-10T16:42:54Z")

</div>

In the query which populates your Flex Repeater, make sure you’re bringing along the `id` column value for each image, and supply this id as a param value.  
 ![20%20AM](https://us1.discourse-cdn.com/inductiveautomation/original/2X/7/75c899f0b468545e645a1c0f79a12c5d5e466f26.png)  
In the View which contains the button, make sure you’re using this `id` value to execute an update query along the lines of

```auto
query = 'DELETE FROM photo_table WHERE id={0};'.format(self.view.params.id)
system.db.runUpdateQuery(query=query, database=<database>)

```

This will only remove the row from the table.

If you then want to refresh the binding of your Flex Repeater, you could use `system.perspective.sendMessage()` ([documentation](https://docs.inductiveautomation.com/display/DOC80/system.perspective.sendMessage)), coupled with a message handler on the Flex Repeater.

---

<div class="post-metadata">

**Author:** ![ptchanchal](https://avatars.discourse-cdn.com/v4/letter/p/f9ae1b/32.png) [@ptchanchal](https://forum.inductiveautomation.com/u/ptchanchal)\
**Post date:** [March 10, 2020, 4:59pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/3 "2020-03-10T16:59:15Z")

</div>

I tried as you told still i am missing something:

Flex repeater instances with id in it:  
 ![1](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/87fa6823e460d7afda20527d643cfd3ee184eb38.png)

id param in view where button is present:  
 ![2](https://us1.discourse-cdn.com/inductiveautomation/original/2X/5/5ad4d0726bd36edb5041343aa608a8354fa1f19c.png)

button onClick event:

 ![4](https://us1.discourse-cdn.com/inductiveautomation/original/2X/2/2bc73ca6d5b00cd7308b39050b2e01a907d5c1a9.png)

on clicking row is not deleting from database

---

<div class="post-metadata">

**Author:** ![cmallonee](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/cmallonee/32/6416_2.png) [@cmallonee](https://forum.inductiveautomation.com/u/cmallonee)\
**Post date:** [March 10, 2020, 5:07pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/4 "2020-03-10T17:07:35Z")

</div>

Are you getting any error in your Gateway logs?

Do you have a default database specified for the project? I see that you removed the database argument form the script call.

Do you actually have a column named “id” as part of the `images2` table?

It _looks_ like you’re correctly applying the id from your query, but I don’t see the query which populates the Flex Repeater so I can’t verify that…

It’s possible that the query I supplied you isn’t working - I didn’t actually test the query because I don’t have all of the pieces set up as you do. You could _try_ supplying the `image_as_bytes` string since you have it and specify that column of the table instead…

---

<div class="post-metadata">

**Author:** ![ptchanchal](https://avatars.discourse-cdn.com/v4/letter/p/f9ae1b/32.png) [@ptchanchal](https://forum.inductiveautomation.com/u/ptchanchal)\
**Post date:** [March 10, 2020, 5:16pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/5 "2020-03-10T17:16:46Z")

</div>

Actually problem is with getting which instances of flex repeater got clicked I tried by changing the delete script for deleting all and its working  
 ![5](https://us1.discourse-cdn.com/inductiveautomation/original/2X/d/d9d81e622259994741f87cf5cd6b11a905be5037.png)  
this code deletes all images in database but I am not able to pass the particular id to the sql statement for deleting that row.

---

<div class="post-metadata">

**Author:** ![cmallonee](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/cmallonee/32/6416_2.png) [@cmallonee](https://forum.inductiveautomation.com/u/cmallonee)\
**Post date:** [March 10, 2020, 5:22pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/6 "2020-03-10T17:22:33Z")

</div>

Don’t attempt to figure out which instance was clicked. The `id` param should correlate to the row in the database:

```auto
    id | image_as_bytes
---------------------------------------------------
    1 | cuabIUcbAOPUcbIOAUbojAUB......
    2 | uviBSEIVUbegovubSOEubOieu......
    3 | sevouBEvouBWeovuBKEFHAUB......
    4 | voUWBEovubWEoviunWHAUB......
    5 | eOUvbweouvbWOUvbJAUB......

```

So you should populate your Flex Repeater’s instances with a query like

```auto
select id, image from images2;

```

---

<div class="post-metadata">

**Author:** ![ptchanchal](https://avatars.discourse-cdn.com/v4/letter/p/f9ae1b/32.png) [@ptchanchal](https://forum.inductiveautomation.com/u/ptchanchal)\
**Post date:** [March 10, 2020, 5:25pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/7 "2020-03-10T17:25:35Z")

</div>

![6](https://us1.discourse-cdn.com/inductiveautomation/original/2X/3/3b256fdc146320b146d60b0e278096ee0e65d852.png)

Flex Repeater’s instances

---

<div class="post-metadata">

**Author:** ![ptchanchal](https://avatars.discourse-cdn.com/v4/letter/p/f9ae1b/32.png) [@ptchanchal](https://forum.inductiveautomation.com/u/ptchanchal)\
**Post date:** [March 10, 2020, 5:28pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/8 "2020-03-10T17:28:55Z")

</div>

i tried printing the id in a label in view and it shows correctly

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 10, 2020, 5:51pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/9 "2020-03-10T17:51:55Z")

</div>

SQL doesn’t have direct access to perspective properties and objects. You must parameterize the query and pass the properties to the query parameters.

---

<div class="post-metadata">

**Author:** ![cmallonee](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/cmallonee/32/6416_2.png) [@cmallonee](https://forum.inductiveautomation.com/u/cmallonee)\
**Post date:** [March 10, 2020, 5:55pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/10 "2020-03-10T17:55:43Z")

</div>

@pturmel: That’s what we’re doing.  
@ptchanchal: if you are able to send me the view.json files for your two Views, I’ll attempt to replicate the problem when I have some time later in the day.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 10, 2020, 6:09pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/11 "2020-03-10T18:09:22Z")

</div>

Ah, brain-freeze. Thought I was looking at the Update query that deletes based on id.

---

<div class="post-metadata">

**Author:** ![ptchanchal](https://avatars.discourse-cdn.com/v4/letter/p/f9ae1b/32.png) [@ptchanchal](https://forum.inductiveautomation.com/u/ptchanchal)\
**Post date:** [March 10, 2020, 6:16pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/12 "2020-03-10T18:16:43Z")

</div>

ya i will send that in between I noticed that its due to data type concatenation issue

![7](https://us1.discourse-cdn.com/inductiveautomation/original/2X/3/377a50c106e235a3b0ddbd672f096b97f172fa37.png)

log:  
 ![8](https://us1.discourse-cdn.com/inductiveautomation/original/2X/e/ec37e529e600ce358ccb94f873ceb0324cff689c.png)

if write a query like:  
query = “DELETE FROM images2 where id = 27”  
it works

And also tried to print the value of id in other label and its giving correct value as required but its not able pass it to sql

the below statement return correct id according to the button clicked but i couldn’t pass it to sql  
self.getSibling(“Label\_0”).props.text= self.getSibling(“Label”).props.text

---

<div class="post-metadata">

**Author:** ![cmallonee](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/cmallonee/32/6416_2.png) [@cmallonee](https://forum.inductiveautomation.com/u/cmallonee)\
**Post date:** [March 10, 2020, 7:34pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/13 "2020-03-10T19:34:23Z")

</div>

Try printing the query before you actually execute it, so that we can see what’s being sent.

```auto
system.perspective.print(query)

```

To fix the TypeError, just wrap the `args` variable as a `str`:

```auto
query = "DELETE from images2 where id=" + str(arg)

```

The Label is working because we wrap everything in Strings behind the scenes.

---

<div class="post-metadata">

**Author:** ![cmallonee](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/cmallonee/32/6416_2.png) [@cmallonee](https://forum.inductiveautomation.com/u/cmallonee)\
**Post date:** [March 10, 2020, 7:42pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/14 "2020-03-10T19:42:10Z")

</div>

Remember when I asked if there were any errors in the logs?

This should have generated an error:

```auto
query = 'DELETE FROM photo_table WHERE id={0};'.format({self.view.params.id})

```

It SHOULD be

```auto
query = 'DELETE FROM photo_table WHERE id={0};'.format(self.view.params.id)

```

---

<div class="post-metadata">

**Author:** ![ptchanchal](https://avatars.discourse-cdn.com/v4/letter/p/f9ae1b/32.png) [@ptchanchal](https://forum.inductiveautomation.com/u/ptchanchal)\
**Post date:** [March 10, 2020, 7:44pm UTC](https://forum.inductiveautomation.com/t/how-to-remove-an-instance-of-flex-repeater-on-button-click/32977/15 "2020-03-10T19:44:36Z")

</div>

Wow! thank you so much it worked, Now refreshing flex repeater is only left