# How to Separate Alarm Tables for Two PLCs in Perspective

**URL:** <https://forum.inductiveautomation.com/t/how-to-separate-alarm-tables-for-two-plcs-in-perspective/112866>\
**Category:** Ignition\
**Tags:** perspective\
**Created:** [December 17, 2025, 2:17pm UTC](https://forum.inductiveautomation.com/t/how-to-separate-alarm-tables-for-two-plcs-in-perspective/112866 "2025-12-17T14:17:34Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![TechEnlive](https://avatars.discourse-cdn.com/v4/letter/t/3be4f8/32.png) [@TechEnlive](https://forum.inductiveautomation.com/u/TechEnlive)\
**Post date:** [December 17, 2025, 2:17pm UTC](https://forum.inductiveautomation.com/t/how-to-separate-alarm-tables-for-two-plcs-in-perspective/112866/1 "2025-12-17T14:17:35Z")

</div>

**Hi team,**

We have two PLCs, and we would like to display a separate Alarm Status Table for each PLC.  
Right now, the Alarm Table shows alarms from both PLCs together.

What is the best way to filter the Alarm Status Table so each PLC only shows its own alarms?

Thanks!

---

<div class="post-metadata">

**Author:** ![tgarrison](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tgarrison/32/80965_2.png) [@tgarrison](https://forum.inductiveautomation.com/u/tgarrison)\
**Post date:** [December 17, 2025, 4:06pm UTC](https://forum.inductiveautomation.com/t/how-to-separate-alarm-tables-for-two-plcs-in-perspective/112866/2 "2025-12-17T16:06:59Z")

</div>

On the alarm status table, there's a Filters.Conditions property. Source/DisplayPath/Provider are all possible. Assuming you have a common part of your tagpath that you can filter against..

---

<div class="post-metadata">

**Author:** ![TechEnlive](https://avatars.discourse-cdn.com/v4/letter/t/3be4f8/32.png) [@TechEnlive](https://forum.inductiveautomation.com/u/TechEnlive)\
**Post date:** [December 17, 2025, 4:15pm UTC](https://forum.inductiveautomation.com/t/how-to-separate-alarm-tables-for-two-plcs-in-perspective/112866/3 "2025-12-17T16:15:45Z")

</div>

Thanks but can you help how configure these parametes.  
as our PLC is “\_Plc\_sch\_“

---

<div class="post-metadata">

**Author:** ![Nol](https://avatars.discourse-cdn.com/v4/letter/n/8e8cbc/32.png) [@Nol](https://forum.inductiveautomation.com/u/Nol)\
**Post date:** [December 17, 2025, 8:35pm UTC](https://forum.inductiveautomation.com/t/how-to-separate-alarm-tables-for-two-plcs-in-perspective/112866/4 "2025-12-17T20:35:06Z")

</div>

Are your tags for the different PLCs in different folders? Put the folder name in the source path. If they're all mixed together then that's a harder problem.

`folderA*`