# IBH Link S7++ connect to ignition

**URL:** <https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499>\
**Category:** Ignition\
**Created:** [April 8, 2024, 8:31am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499 "2024-04-08T08:31:38Z")\
**Posts on this page:** 11\
**Page:** 1

<div class="post-metadata">

**Author:** ![Molnar\_Bence](https://avatars.discourse-cdn.com/v4/letter/m/c68b51/32.png) [@Molnar\_Bence](https://forum.inductiveautomation.com/u/Molnar_Bence)\
**Post date:** [April 8, 2024, 8:31am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/1 "2024-04-08T08:31:38Z")

</div>

Hi guys,

I would like to connect the VIPA PLC (Vipa 315-2ag12) to Ignition with IHB Link S7++.

The IBH Link is all default settings just the IP address is different. In the network I can ping this IP address, but the Ignition can't connect this PLC.

In the Ignition, the device connection is all default setting. I select the S7-300 PLC and set the right IP address.

My question is, where and what should I setting to make this a good? On the IBH Links or on the Vipa PLC or on the ignition?

I am really new in the Ignition programming so I am really open any idea!  
If you need more information just write it!

Thank you!

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [April 9, 2024, 8:03am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/2 "2024-04-09T08:03:16Z")

</div>

Have you seen [this](https://forum.inductiveautomation.com/t/siemens-s7-200-ignition/45163/6)?

---

<div class="post-metadata">

**Author:** ![Molnar\_Bence](https://avatars.discourse-cdn.com/v4/letter/m/c68b51/32.png) [@Molnar\_Bence](https://forum.inductiveautomation.com/u/Molnar_Bence)\
**Post date:** [April 9, 2024, 8:54am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/4 "2024-04-09T08:54:59Z")

</div>

Yes, I saw that before. In your config have "Own station address: 10" this is important or not? Because in my config it is 0.

 ![20240409_104952](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/6/864a5919d243b4794cba2bed087a32974b96345e.jpeg)

And can I connect the VIPA PLC to Ignition over the MPI?

Thank you for your help!!

---

<div class="post-metadata">

**Author:** ![Arnaud\_Declerck](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/arnaud_declerck/32/44872_2.png) [@Arnaud\_Declerck](https://forum.inductiveautomation.com/u/Arnaud_Declerck)\
**Post date:** [April 9, 2024, 9:05am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/5 "2024-04-09T09:05:58Z")

</div>

The Own device address is the address that the IBH will have on the MPI/PPI bus. If the 0 already exist, then you would not be able to communicate.

---

<div class="post-metadata">

**Author:** ![Molnar\_Bence](https://avatars.discourse-cdn.com/v4/letter/m/c68b51/32.png) [@Molnar\_Bence](https://forum.inductiveautomation.com/u/Molnar_Bence)\
**Post date:** [April 9, 2024, 9:06am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/6 "2024-04-09T09:06:29Z")

</div>

And can I set something in the PLC?

---

<div class="post-metadata">

**Author:** ![Molnar\_Bence](https://avatars.discourse-cdn.com/v4/letter/m/c68b51/32.png) [@Molnar\_Bence](https://forum.inductiveautomation.com/u/Molnar_Bence)\
**Post date:** [April 9, 2024, 9:25am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/7 "2024-04-09T09:25:21Z")

</div>

Port 0 is not occupied. So that is why I think the 0 is good for me.

---

<div class="post-metadata">

**Author:** ![Arnaud\_Declerck](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/arnaud_declerck/32/44872_2.png) [@Arnaud\_Declerck](https://forum.inductiveautomation.com/u/Arnaud_Declerck)\
**Post date:** [April 9, 2024, 9:57am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/8 "2024-04-09T09:57:45Z")

</div>

Can you go online with the programming software?

---

<div class="post-metadata">

**Author:** ![Molnar\_Bence](https://avatars.discourse-cdn.com/v4/letter/m/c68b51/32.png) [@Molnar\_Bence](https://forum.inductiveautomation.com/u/Molnar_Bence)\
**Post date:** [April 9, 2024, 10:04am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/9 "2024-04-09T10:04:25Z")

</div>

Usually, I do this with the PC adapter via MPI, but if this module is inserted, I can also connect to the PLC via Ethernet through the module and program it.

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [April 9, 2024, 10:13am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/10 "2024-04-09T10:13:18Z")

</div>

~~Have you done [this](https://support.inductiveautomation.com/hc/en-us/articles/360047576831-Connecting-to-Siemens-S7-1200-and-S7-1500) in the HW config on the PLC (and downloaded)?~~  
Edit: I was to fast... this is S7-300...

Are there any messages in the Ignition Gateway logs?

---

<div class="post-metadata">

**Author:** ![Molnar\_Bence](https://avatars.discourse-cdn.com/v4/letter/m/c68b51/32.png) [@Molnar\_Bence](https://forum.inductiveautomation.com/u/Molnar_Bence)\
**Post date:** [April 16, 2024, 8:22am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/11 "2024-04-16T08:22:30Z")

</div>

Thanks you for your help!

I tried before this with trial version, but now I tired with complete licence and it works now!  
All settings is default. Connected and works!

Does it matter if I wanted to connect to the device with a licensed version?

Thank you!

---

<div class="post-metadata">

**Author:** ![zxcslo](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/zxcslo/32/61610_2.png) [@zxcslo](https://forum.inductiveautomation.com/u/zxcslo)\
**Post date:** [April 16, 2024, 8:37am UTC](https://forum.inductiveautomation.com/t/ibh-link-s7-connect-to-ignition/88499/12 "2024-04-16T08:37:36Z")

</div>

> [@Molnar\_Bence](#):
>
> Does it matter if I wanted to connect to the device with a licensed version?

No, it doesn't.  
In Trial, Ignition is running for 2 hours, after that YOU have to manually reset the trial to start again... if you don't, then nothing works...