# IEC 61850 alarm time

**URL:** <https://forum.inductiveautomation.com/t/iec-61850-alarm-time/90647>\
**Category:** Ignition\
**Tags:** perspective\
**Created:** [May 21, 2024, 12:28am UTC](https://forum.inductiveautomation.com/t/iec-61850-alarm-time/90647 "2024-05-21T00:28:32Z")\
**Posts on this page:** 1\
**Showing post:** 3

<div class="post-metadata">

**Author:** ![tevis](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tevis/32/40783_2.png) [@tevis](https://forum.inductiveautomation.com/u/tevis)\
**Post date:** [August 12, 2025, 2:09am UTC](https://forum.inductiveautomation.com/t/iec-61850-alarm-time/90647/3 "2025-08-12T02:09:10Z")

</div>

You can set the Alarm Timestamp source, and ensure that you are also subscribed to the relevent \_t tag.

eg: subscribe to the following:

- {BUFFERED REPORT PATH}.PRO\_BK1XCBR1.Pos.stVal
- {BUFFERED REPORT PATH}.PRO\_BK1XCBR1.Pos.t

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/4/a47edf4da5fbe69b3fadb61eccf20273f449a795.png)

> [@IEC61850 Alarm Time Delay](https://forum.inductiveautomation.com/t/iec61850-alarm-time-delay/109623):
>
> Hi there, I have configured IEC61850 based alarms for CB position feedback. I am also receiving the timestamp from the IED. These are both part of a IEC61850 Buffered Report. My issue is that the status tag updates slightly before the timestamp, (1-2s when viewing in designer). This results in my alarms having the timestamp of the previous change of state. Adding a time delay to the alarm does not seem to rectify this. I have included screenshot showing ignition alarm status table, and the …

---