# IEC61850 Alarm Time Delay

**URL:** <https://forum.inductiveautomation.com/t/iec61850-alarm-time-delay/109623>\
**Category:** Ignition\
**Created:** [August 12, 2025, 2:06am UTC](https://forum.inductiveautomation.com/t/iec61850-alarm-time-delay/109623 "2025-08-12T02:06:00Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![tevis](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tevis/32/40783_2.png) [@tevis](https://forum.inductiveautomation.com/u/tevis)\
**Post date:** [August 12, 2025, 2:06am UTC](https://forum.inductiveautomation.com/t/iec61850-alarm-time-delay/109623/1 "2025-08-12T02:06:01Z")

</div>

Hi there,

I have configured IEC61850 based alarms for CB position feedback. I am also receiving the timestamp from the IED.

These are both part of a IEC61850 Buffered Report.

My issue is that the status tag updates slightly before the timestamp, (1-2s when viewing in designer). This results in my alarms having the timestamp of the previous change of state.

Adding a time delay to the alarm does not seem to rectify this.

I have included screenshot showing ignition alarm status table, and the Sequential Event Reports as exported from the IED.

Interested to see if anyone has seen this on 61850 or DNP3

- Trigger alarm based on change of timestamp?

Thanks!

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/2/a23ca022be778898f5d90b45e6f91449946e4d94.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/9/d926e5fc14a40623ba16712f4bdac20b4a0545e1.png)

---

<div class="post-metadata">

**Author:** ![Chris\_Bingham](https://avatars.discourse-cdn.com/v4/letter/c/e5b9ba/32.png) [@Chris\_Bingham](https://forum.inductiveautomation.com/u/Chris_Bingham)\
**Post date:** [August 12, 2025, 12:37pm UTC](https://forum.inductiveautomation.com/t/iec61850-alarm-time-delay/109623/2 "2025-08-12T12:37:03Z")

</div>

I haven’t used the IEC driver, but I see there’s a setting on the driver under [Misc. Advanced Settings](https://www.docs.inductiveautomation.com/docs/8.1/ignition-modules/opc-ua/opc-ua-drivers/iec-61850-driver#misc-advanced-settings) related to timestamp source:

> Use Report Timestamp : Determines if the timestamp from the report will be used instead of the timestamp associated with each reported value.