# \[IGN-14144\] S7-1200 G2 with new Siemens Driver

**URL:** <https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241>\
**Category:** Ignition 8.3 Early Access\
**Created:** [August 28, 2025, 1:50pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241 "2025-08-28T13:50:34Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![billy\_hanner](https://avatars.discourse-cdn.com/v4/letter/b/258eb7/32.png) [@billy\_hanner](https://forum.inductiveautomation.com/u/billy_hanner)\
**Post date:** [August 28, 2025, 1:50pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/1 "2025-08-28T13:50:34Z")

</div>

Has anyone got ignition to work with the new S7-1200 Generation 2s

I know they are supposed to be closer to a 1500 then a 1200 but neither option appears to work on symbolic

I’ve had no luck so far when trying to use symbolic addressing so wondering if anyone else has got this to work?

---

<div class="post-metadata">

**Author:** ![Cody\_Morgan](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@Cody\_Morgan](https://forum.inductiveautomation.com/u/Cody_Morgan)\
**Post date:** [August 28, 2025, 2:03pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/2 "2025-08-28T14:03:33Z")

</div>

We’ve not tested internally, yet. Let me look around to see if there’s any info about them.

What sort of logs are you getting with the Siemens loggers set to Debug?

---

<div class="post-metadata">

**Author:** ![billy\_hanner](https://avatars.discourse-cdn.com/v4/letter/b/258eb7/32.png) [@billy\_hanner](https://forum.inductiveautomation.com/u/billy_hanner)\
**Post date:** [August 28, 2025, 2:32pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/3 "2025-08-28T14:32:17Z")

</div>

Hi Cody,

No worries please find the logs below

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/5/b53f253cc181d476c0ab744a042d58ba6d88aac0.png)

Detailed breakdown on the connection errors

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/e/4ef3cf28a5544f959bff09a466f2faf12a46bf56.png)

Apparently according to siemens they are very similar to a S7-1500 so if you just pick the S7-1500 option they will work with most things 😅 heard that before

---

<div class="post-metadata">

**Author:** ![Cody\_Morgan](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@Cody\_Morgan](https://forum.inductiveautomation.com/u/Cody_Morgan)\
**Post date:** [August 28, 2025, 3:05pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/4 "2025-08-28T15:05:22Z")

</div>

Thanks! The logs suggest that the library we use is unable to detect the PLC type. We're trying to get our hands on one to test internally, but assuming your PLC and device connection are configured appropriately, there is probably nothing you can change on your end to get symbolic access working.

---

<div class="post-metadata">

**Author:** ![billy\_hanner](https://avatars.discourse-cdn.com/v4/letter/b/258eb7/32.png) [@billy\_hanner](https://forum.inductiveautomation.com/u/billy_hanner)\
**Post date:** [August 28, 2025, 3:34pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/5 "2025-08-28T15:34:18Z")

</div>

> [@Cody\_Morgan](#):
>
> hat the library we use is unable to detect the PLC type. We're trying to get our hands on one to test internally, but assuming your PLC and device connection are configured appropriately, there is probably nothing you can change on your end to get symbolic access working.

I’ve used the same setup as the S7-1500 so I’m assuming it’s all correct.

No worries. Are there any log files or other information I can provide that might help? While you're trying to get your hands on one?

---

<div class="post-metadata">

**Author:** ![Cody\_Morgan](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@Cody\_Morgan](https://forum.inductiveautomation.com/u/Cody_Morgan)\
**Post date:** [August 28, 2025, 3:41pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/6 "2025-08-28T15:41:00Z")

</div>

Not that I know of, but I'm still digging. Thanks for the offer, I'll let you know!

---

<div class="post-metadata">

**Author:** ![billy\_hanner](https://avatars.discourse-cdn.com/v4/letter/b/258eb7/32.png) [@billy\_hanner](https://forum.inductiveautomation.com/u/billy_hanner)\
**Post date:** [August 28, 2025, 4:04pm UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/7 "2025-08-28T16:04:07Z")

</div>

> [@Cody\_Morgan](#):
>
> ary we use is unable to detect the PLC type. We're trying to get our hands on one to test internally, but assuming your PLC and device connection are configured appropriately, there is probably nothing you can change on your end to get symbolic access working.

No worries i’ll mark this thread as solved but feel free to get in contact if i can help

---

<div class="post-metadata">

**Author:** ![shakouriniaasghar](https://avatars.discourse-cdn.com/v4/letter/s/50afbb/32.png) [@shakouriniaasghar](https://forum.inductiveautomation.com/u/shakouriniaasghar)\
**Post date:** [December 27, 2025, 12:37am UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/8 "2025-12-27T00:37:38Z")

</div>

Hello,  
has any solution been provided for this issue?  
I have encountered the same problem as well.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [December 27, 2025, 12:38am UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/9 "2025-12-27T00:38:46Z")

</div>

The underlying S7 library needed to be updated with support for the new G2.

8.3.3 or 8.3.4 will have a new version of module with the updated library and support.

---

<div class="post-metadata">

**Author:** ![shakouriniaasghar](https://avatars.discourse-cdn.com/v4/letter/s/50afbb/32.png) [@shakouriniaasghar](https://forum.inductiveautomation.com/u/shakouriniaasghar)\
**Post date:** [December 27, 2025, 12:57am UTC](https://forum.inductiveautomation.com/t/ign-14144-s7-1200-g2-with-new-siemens-driver/110241/10 "2025-12-27T00:57:27Z")

</div>

Thank you, Kevin.Herron.  
After updating to version 8.4, the connection with the G series was successfully established.  
I sincerely appreciate your support and guidance.