I feel that the dataset tag is a little redundant. I know where you're coming from, you want to avoid manually adding in the fault messages into the tags. I don't see much of a performance hit on this method though. Just make sure your scan classes are reasonable.

Look into using tag import for your tags. Keep a master list in a spreadsheet and make an export tool/script to output xml to put in your tags. Then just import all of your tags, even if just one alarm changes or is added.

> [@Efficient way to import 500+ alarms into ignition from Allen Bradly plc](https://forum.inductiveautomation.com/t/efficient-way-to-import-500-alarms-into-ignition-from-allen-bradly-plc/72445/9):
>
> HMI alarms list from FactoryTalk View ME Studio. From what I understand, Ignition's OPC Server, and any other non-Rockwell OPC server, doesn't support Rockwell's Alarms and Events feature (at their current states).

---