I just installed Ignition 7.9.2 to work on an older project.

However, when starting up the gateway I keep getting what looks like java errors.

First  
`Unrecognized VM option 'UseConcMarkSweepGC'`

Then  
`Unrecognized VM option 'CMSClassUnloadingEnabled'`

I have Java 8 installed. Is this a PATH issue?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [March 31, 2025, 3:47pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/2 "2025-03-31T15:47:07Z")

</div>

Yes. Your gateway is running with a newer java. (You should also get rid of those VM options and use G1GC.)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2025, 3:47pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/3 "2025-03-31T15:47:14Z")

</div>

> [@amarks](#):
>
> I have Java 8 installed. Is this a PATH issue?

It might be, because those options should be recognized by JDK 8.

What happens if you open a terminal / cmd prompt and run `java -version`?

---

<div class="post-metadata">

**Author:** ![amarks](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/amarks/32/45610_2.png) [@amarks](https://forum.inductiveautomation.com/u/amarks)\
**Post date:** [March 31, 2025, 3:58pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/4 "2025-03-31T15:58:13Z")

</div>

1.8.0\_402

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2025, 3:59pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/5 "2025-03-31T15:59:46Z")

</div>

Can you upload the ignition.conf file?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2025, 4:01pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/6 "2025-03-31T16:01:10Z")

</div>

> [@Kevin.Herron](#):
>
> What happens if you open a terminal / cmd prompt and run `java -version`?

also in case it needs to be said, this needs to be done on the machine that's actually running the Ignition Gateway.

---

<div class="post-metadata">

**Author:** ![amarks](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/amarks/32/45610_2.png) [@amarks](https://forum.inductiveautomation.com/u/amarks)\
**Post date:** [March 31, 2025, 4:10pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/7 "2025-03-31T16:10:56Z")

</div>

> [@Kevin.Herron](#):
>
> > [@Kevin.Herron](#):
> >
> > What happens if you open a terminal / cmd prompt and run `java -version`?
> 
> also in case it needs to be said, this needs to be done on the machine that's actually running the Ignition Gateway.

Yes, it was.

```python
#encoding=UTF-8
# Configuration files must begin with a line specifying the encoding
# of the the file.

# ********************************************************************
# Wrapper License Properties (Ignored by Community Edition)
# ********************************************************************
# Professional and Standard Editions of the Wrapper require a valid
# License Key to start. Licenses can be purchased or a trial license
# requested on the following pages:
# http://wrapper.tanukisoftware.com/purchase
# http://wrapper.tanukisoftware.com/trial

# Include file problems can be debugged by removing the first '#'
# from the following line:
##include.debug

# The Wrapper will look for either of the following optional files for a
# valid License Key. License Key properties can optionally be included
# directly in this configuration file.
#include ./wrapper-license.conf

# The following property will output information about which License Key(s)
# are being found, and can aid in resolving any licensing problems.
#wrapper.license.debug=TRUE

# ********************************************************************
# Wrapper Localization
# ********************************************************************
# Specify the locale which the Wrapper should use. By default the system
# locale is used.
#wrapper.lang=en_US # en_US or ja_JP

# Specify the location of the Wrapper's language resources. If these are
# missing, the Wrapper will default to the en_US locale.
wrapper.lang.folder=../lang

# ********************************************************************
# Wrapper Java Properties
# ********************************************************************
# Java Application
# Locate the java binary on the system PATH:
wrapper.java.command=C:/Program Files/Zulu/zulu-21/bin/java.exe
# Specify a specific java binary:
#set.JAVA_HOME=/java/path
#wrapper.java.command=C:/Program Files/Zulu/zulu-21/bin/java.exe

# Tell the Wrapper to log the full generated Java command line.
#wrapper.java.command.loglevel=INFO

# Java Main class. This class must implement the WrapperListener interface
# or guarantee that the WrapperManager class is initialized. Helper
# classes are provided to do this for you. See the Integration section
# of the documentation for details.
wrapper.java.mainclass=org.tanukisoftware.wrapper.WrapperSimpleApp

# Java Classpath (include wrapper.jar) Add class path elements as
# needed starting from 1
wrapper.java.classpath.1=lib/wrapper.jar
wrapper.java.classpath.2=lib/catapult.jar

# Java Library Path (location of Wrapper.DLL or libwrapper.so)
wrapper.java.library.path.1=lib

# Java Bits. On applicable platforms, tells the JVM to run in 32 or 64-bit mode.
wrapper.java.additional.auto_bits=TRUE

# Java Additional Parameters
wrapper.java.additional.1=-XX:+UseConcMarkSweepGC
wrapper.java.additional.2=-XX:+CMSClassUnloadingEnabled
wrapper.java.additional.3=-Ddata.dir=data
wrapper.java.additional.4=-Dorg.apache.catalina.loader.WebappClassLoader.ENABLE_CLEAR_REFERENCES=false
#wrapper.java.additional.5=-Xdebug
#wrapper.java.additional.6=-Xrunjdwp:transport=dt_socket,server=y,suspend=n,address=8000

# Initial Java Heap Size (in MB)
wrapper.java.initmemory=1024

# Maximum Java Heap Size (in MB)
wrapper.java.maxmemory=2048

# Application parameters. Add parameters as needed starting from 1
wrapper.app.parameter.1=com.inductiveautomation.catapult.Catapult

wrapper.shutdown.timeout=120
wrapper.jvm_exit.timeout=120

# Set this value to TRUE to allow ignition.conf to be reloaded when the JVM is restarted
wrapper.restart.reload_configuration=TRUE

# ********************************************************************
# Wrapper Logging Properties
# ********************************************************************
# Enables Debug output from the Wrapper.
# wrapper.debug=TRUE

# Format of output for the console. (See docs for formats)
wrapper.console.format=PM

# Log Level for console output. (See docs for log levels)
wrapper.console.loglevel=INFO

# Log file to use for wrapper output logging.
wrapper.logfile=logs/wrapper.log

# Format of output for the log file. (See docs for formats)
wrapper.logfile.format=LPTM

# Log Level for log file output. (See docs for log levels)
wrapper.logfile.loglevel=INFO

# Maximum size that the log file will be allowed to grow to before
# the log is rolled. Size is specified in bytes. The default value
# of 0, disables log rolling. May abbreviate with the 'k' (kb) or
# 'm' (mb) suffix. For example: 10m = 10 megabytes.
wrapper.logfile.maxsize=10m

# Maximum number of rolled log files which will be allowed before old
# files are deleted. The default value of 0 implies no limit.
wrapper.logfile.maxfiles=5

# Log Level for sys/event log output. (See docs for log levels)
wrapper.syslog.loglevel=NONE

# ********************************************************************
# Wrapper General Properties
# ********************************************************************
# Allow for the use of non-contiguous numbered properties
wrapper.ignore_sequence_gaps=TRUE

# Title to use when running as a console
wrapper.console.title=Ignition Gateway

# ********************************************************************
# Wrapper JVM Checks
# ********************************************************************
# Detect DeadLocked Threads in the JVM. (Requires Standard Edition)
#wrapper.check.deadlock=TRUE
#wrapper.check.deadlock.interval=60
#wrapper.check.deadlock.action=RESTART
#wrapper.check.deadlock.output=FULL

# Out Of Memory detection.
#wrapper.filter.trigger.1000=java.lang.OutOfMemoryError
#wrapper.filter.action.1000=RESTART
#wrapper.filter.message.1000=The JVM has run out of memory.

wrapper.on_exit.default=SHUTDOWN
wrapper.on_exit.2=RESTART

# ********************************************************************
# Wrapper Email Notifications. (Requires Professional Edition)
# ********************************************************************
# Common Event Email settings.
#wrapper.event.default.email.debug=TRUE
#wrapper.event.default.email.smtp.host=<SMTP_Host>
#wrapper.event.default.email.smtp.port=25
#wrapper.event.default.email.subject=[%WRAPPER_HOSTNAME%:%WRAPPER_NAME%:%WRAPPER_EVENT_NAME%] Event Notification
#wrapper.event.default.email.sender=<Sender email>
#wrapper.event.default.email.recipient=<Recipient email>

# Configure the log attached to event emails.
#wrapper.event.default.email.attach_log=TRUE
#wrapper.event.default.email.maillog.lines=50
#wrapper.event.default.email.maillog.format=LPTM
#wrapper.event.default.email.maillog.loglevel=INFO

# Enable specific event emails.
#wrapper.event.wrapper_start.email=TRUE
#wrapper.event.jvm_prelaunch.email=TRUE
#wrapper.event.jvm_start.email=TRUE
#wrapper.event.jvm_started.email=TRUE
#wrapper.event.jvm_deadlock.email=TRUE
#wrapper.event.jvm_stop.email=TRUE
#wrapper.event.jvm_stopped.email=TRUE
#wrapper.event.jvm_restart.email=TRUE
#wrapper.event.jvm_failed_invocation.email=TRUE
#wrapper.event.jvm_max_failed_invocations.email=TRUE
#wrapper.event.jvm_kill.email=TRUE
#wrapper.event.jvm_killed.email=TRUE
#wrapper.event.jvm_unexpected_exit.email=TRUE
#wrapper.event.wrapper_stop.email=TRUE

# Specify custom mail content
wrapper.event.jvm_restart.email.body=The JVM was restarted.\n\nPlease check on its status.\n

# ********************************************************************
# Wrapper Windows NT/2000/XP Service Properties
# ********************************************************************
# WARNING - Do not modify any of these properties when an application
# using this configuration file has been installed as a service.
# Please uninstall the service before modifying this section. The
# service can then be reinstalled.

# Name of the service
wrapper.name=Ignition

# Display name of the service
wrapper.displayname=Ignition Gateway

# Description of the service
wrapper.description=Ignition Gateway

# Service dependencies. Add dependencies as needed starting from 1
wrapper.ntservice.dependency.1=

# Mode in which the service is installed. AUTO_START, DELAY_START or DEMAND_START
wrapper.ntservice.starttype=AUTO_START

# Allow the service to interact with the desktop.
wrapper.ntservice.interactive=false

#VERSION - DO NOT MODIFY: 7

```

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2025, 4:13pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/8 "2025-03-31T16:13:51Z")

</div>

> [@amarks](#):
>
> `wrapper.java.command=C:/Program Files/Zulu/zulu-21/bin/java.exe`

Well then...

---

<div class="post-metadata">

**Author:** ![amarks](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/amarks/32/45610_2.png) [@amarks](https://forum.inductiveautomation.com/u/amarks)\
**Post date:** [March 31, 2025, 4:31pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/9 "2025-03-31T16:31:49Z")

</div>

That doesn't mean much to me

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2025, 4:35pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/10 "2025-03-31T16:35:42Z")

</div>

It's pointing to a Java 21 install.

Change the path so it points to wherever you have JDK 8 installed.

You can also comment it out to let Ignition use whatever it finds on the PATH variable.

---

<div class="post-metadata">

**Author:** ![amarks](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/amarks/32/45610_2.png) [@amarks](https://forum.inductiveautomation.com/u/amarks)\
**Post date:** [March 31, 2025, 5:33pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/11 "2025-03-31T17:33:45Z")

</div>

I previously had 8.1 installed. Could that affect this?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 31, 2025, 5:34pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/12 "2025-03-31T17:34:24Z")

</div>

No, Ignition 8 includes its own Java runtime, it doesn’t install or need one from your system.

---

<div class="post-metadata">

**Author:** ![amarks](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/amarks/32/45610_2.png) [@amarks](https://forum.inductiveautomation.com/u/amarks)\
**Post date:** [March 31, 2025, 5:35pm UTC](https://forum.inductiveautomation.com/t/ignition-7-9-and-java-install/104462/13 "2025-03-31T17:35:30Z")

</div>

Ok. Updating the path in the conf file to

`C:/Program Files/Zulu/zulu-8-jre/bin/java.exe`

worked

Service is now started