Hello,

I dragged and dropped a 61850 report tag from the OPC Quick Client and created a tag with this address:

ns=1;s=[MVDFB\_52FB02\_FPR]MVDFB\_52FB02\_FPRSYSTEM/LLN0. **brcbA01** $MVDFB\_52FB02\_FPRCONTROL/CATS1.BatShrt.stVal

Within the SCD file, we have reports brcbA01, brcbA02, brcbA03, and brcbA04. However, it seems like the brcbA04 report is being enabled and used by Ignition every time the 61850 device in Ignition is enabled even though the OPC Item Path is pointing at brcbA01.

When I subscribe to the report brcbA04 with another device entirely, Ignition drops all of my tag connections that are connected to report brcbA01 and displays:

Bad("Bad\_OutOfService: The source of the data is not operational.")

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 1, 2023, 9:18pm UTC](https://forum.inductiveautomation.com/t/ignition-8-1-28-61850-driver-defaults-to-report-4-brcba04/78690/2 "2023-09-01T21:18:16Z")

</div>

A few things might that might help diagnose this:

1. disable any other 61850 devices and tags
2. enable DEBUG or TRACE level logging for loggers you find under "com.inductiveautomation.ignition.drivers.iec61850" (see [Diagnostics - Logs - Ignition User Manual 8.1 - Ignition Documentation](https://docs.inductiveautomation.com/display/DOC81/Diagnostics+-+Logs#DiagnosticsLogs-ChangingLoggingLevels))
3. separate from this, just find these report blocks in the gateway OPC Quick Client, under the "Model" folder, and read the `RptID` value of each of these blocks.

---

<div class="post-metadata">

**Author:** ![Mike\_Le](https://avatars.discourse-cdn.com/v4/letter/m/3ec8ea/32.png) [@Mike\_Le](https://forum.inductiveautomation.com/u/Mike_Le)\
**Post date:** [September 5, 2023, 10:50pm UTC](https://forum.inductiveautomation.com/t/ignition-8-1-28-61850-driver-defaults-to-report-4-brcba04/78690/3 "2023-09-05T22:50:03Z")

</div>

I've tried the above steps, and it is still pulling from report 4 even when I try report 1, 2, & 3.

Log does not show anything out of the ordinary:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/4/b403cd5bcbbcba18fba7635c4e3c99147baa1c7a.png)  
Neither does checking RptID in the OPC Quick Client:  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/7/87abf55494c5bff6b91617a2e709d823ae8344ce.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 6, 2023, 12:51am UTC](https://forum.inductiveautomation.com/t/ignition-8-1-28-61850-driver-defaults-to-report-4-brcba04/78690/4 "2023-09-06T00:51:18Z")

</div>

Read and compare the `RptID` value for each of the blocks.

Those loggers need to be set before you subscribe to something. They'll definitely show up.

Probably best if you call support and let them look over your shoulder. They can also get the SCL file from you as well if we need to try to reproduce.

---

<div class="post-metadata">

**Author:** ![Mike\_Le](https://avatars.discourse-cdn.com/v4/letter/m/3ec8ea/32.png) [@Mike\_Le](https://forum.inductiveautomation.com/u/Mike_Le)\
**Post date:** [September 6, 2023, 3:46pm UTC](https://forum.inductiveautomation.com/t/ignition-8-1-28-61850-driver-defaults-to-report-4-brcba04/78690/5 "2023-09-06T15:46:56Z")

</div>

How do I set the loggers?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [September 6, 2023, 3:55pm UTC](https://forum.inductiveautomation.com/t/ignition-8-1-28-61850-driver-defaults-to-report-4-brcba04/78690/6 "2023-09-06T15:55:28Z")

</div>

> [@Kevin.Herron](#):
>
> enable DEBUG or TRACE level logging for loggers you find under "com.inductiveautomation.ignition.drivers.iec61850" (see [Diagnostics - Logs - Ignition User Manual 8.1 - Ignition Documentation](https://docs.inductiveautomation.com/display/DOC81/Diagnostics+-+Logs#DiagnosticsLogs-ChangingLoggingLevels))

I linked you to the user manual page that talks about it.

---

<div class="post-metadata">

**Author:** ![tevis](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/tevis/32/40783_2.png) [@tevis](https://forum.inductiveautomation.com/u/tevis)\
**Post date:** [August 12, 2025, 2:36am UTC](https://forum.inductiveautomation.com/t/ignition-8-1-28-61850-driver-defaults-to-report-4-brcba04/78690/7 "2025-08-12T02:36:50Z")

</div>

Seconding Kevin’s response about confirming the Report ID’s.

When you create new report control blocks within Brodersen RTU32, it will increment the Report name, However the auto-generated report ID is the same for all unbuffered report control blocks - I wouldn’t be suprised if other OEM’s had similar quirks.

Created exactly the same issues as above.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/1/01b3529838608288f81a327e50399e354607b252.png)