# Ignition 8.1.5 OPC UA Client Good\_Overload Quality

**URL:** <https://forum.inductiveautomation.com/t/ignition-8-1-5-opc-ua-client-good-overload-quality/46792>\
**Category:** Ignition\
**Created:** [May 17, 2021, 7:14pm UTC](https://forum.inductiveautomation.com/t/ignition-8-1-5-opc-ua-client-good-overload-quality/46792 "2021-05-17T19:14:15Z")\
**Posts on this page:** 1\
**Showing post:** 2

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [May 18, 2021, 2:01pm UTC](https://forum.inductiveautomation.com/t/ignition-8-1-5-opc-ua-client-good-overload-quality/46792/2 "2021-05-18T14:01:49Z")

</div>

Starting in 8.1.2 Ignition’s QualityCode system gained a `Good_Overload` code that is now mapped to when a `Good_Overload` StatusCode is received from an OPC UA server.

You were likely _always_ receiving this StatusCode on value changes from this server but previously it was just ignored.

Slow down your sampling rate (Tag Group rate in Ignition) or just ignore it. The QualityCode is purely informative, it doesn’t have any representation in the tag browser or the quality overlay system.

---

_[View the full topic](https://forum.inductiveautomation.com/t/ignition-8-1-5-opc-ua-client-good-overload-quality/46792)._