Hi there,

I notice that if an alarm is cleared it stops the alarm pipeline even if its not been acknowledged. The use case i am working with requires the pipeline to continue to operator until the alarm has been acknowledged even if its been cleared. Is there a way to do this?

---

<div class="post-metadata">

**Author:** ![pascal.fragnoud](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pascal.fragnoud/32/24728_2.png) [@pascal.fragnoud](https://forum.inductiveautomation.com/u/pascal.fragnoud)\
**Post date:** [April 21, 2023, 6:10pm UTC](https://forum.inductiveautomation.com/t/ignition-alarm-pipeline-question/72774/2 "2023-04-21T18:10:51Z")

</div>

You can configure the drop conditions in the pipeline editor:  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/e/4e0225065a9e05b3f7d5fb991b4d931226eeb2ec.png)