# Ignition Client Performance Issues

**URL:** <https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120>\
**Category:** Ignition\
**Created:** [January 11, 2024, 4:22pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120 "2024-01-11T16:22:52Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![Stephen\_Smith](https://avatars.discourse-cdn.com/v4/letter/s/f1d935/32.png) [@Stephen\_Smith](https://forum.inductiveautomation.com/u/Stephen_Smith)\
**Post date:** [January 11, 2024, 4:22pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120/1 "2024-01-11T16:22:52Z")

</div>

New to ignition so please be kind. The system has been running for several months and about a month ago production has reported that the system is "slow" and that the clients "freeze" and must be re-started at least daily. I did not design the system, it was done by an engineering firm that no longer works for us.  
Below are the details that I have gathered:

1. Number of device connections : 6 (Allen Bradley L8x PLC's)
2. Number of Tags : 162,843
3. Frequency of tag polling : 5 second (I have tried lowering this but when I do the device aggregate statistics "overload" increases from 1% to 85%)
4. Number of concurrent clients : 4 (except when troubleshooting and at that time I will launch a client so I can observe)  
In terms of architecture we are running a primary server, a backup server and a historical. All servers are Dell PowerEdge R340 with Intel Xeon CPU @ 3.70 and 32 GB RAM. Server resource monitor shows CPU usage to be around 1% usage and memory around 80% max.

Thoughts on improving performance and reliability?

---

<div class="post-metadata">

**Author:** ![YF129701](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/yf129701/32/60498_2.png) [@YF129701](https://forum.inductiveautomation.com/u/YF129701)\
**Post date:** [January 11, 2024, 4:23pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120/2 "2024-01-11T16:23:58Z")

</div>

Vision or Perspective?

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [January 11, 2024, 4:26pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120/3 "2024-01-11T16:26:53Z")

</div>

Also, what version of Ignition?

---

<div class="post-metadata">

**Author:** ![Stephen\_Smith](https://avatars.discourse-cdn.com/v4/letter/s/f1d935/32.png) [@Stephen\_Smith](https://forum.inductiveautomation.com/u/Stephen_Smith)\
**Post date:** [January 11, 2024, 4:33pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120/4 "2024-01-11T16:33:46Z")

</div>

Vision

---

<div class="post-metadata">

**Author:** ![Stephen\_Smith](https://avatars.discourse-cdn.com/v4/letter/s/f1d935/32.png) [@Stephen\_Smith](https://forum.inductiveautomation.com/u/Stephen_Smith)\
**Post date:** [January 11, 2024, 4:34pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120/5 "2024-01-11T16:34:47Z")

</div>

8.1.27

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 11, 2024, 4:37pm UTC](https://forum.inductiveautomation.com/t/ignition-client-performance-issues/84120/6 "2024-01-11T16:37:14Z")

</div>

1. That's a painful load situation for a reasonable number of tags. You should study this topic and some of the links therein:

> [@Cannot read some tags inside Rockwell AOI](https://forum.inductiveautomation.com/t/cannot-read-some-tags-inside-rockwell-aoi/38393):
>
> I am trying to see tags inside an AOI. I went back to basics and dragged and dropped the tags from the OPC browser into the Tags Folder, but the quality is bad and there is a red x next to them. What is more confusing is that some are working and some are not. I cannot see any similarities between the few that aren’t working. Data type, In and Out types are working and not working. I can create a new UDT as an In/Out but this seems cumbersome. In this case, I would need to create tags only fo…

You may also find this topic helpful:

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190):
>
> Automation Professionals is pleased to announce its latest EtherNet/IP Communications Suite driver module, a major upgrade to its EtherNet/IP Class1 Communications module, as a Public Beta. As of April 15, 2023, this is now a Production Release. The primary new feature is its new Generic EtherNet/IP Client Driver, a drop-in replacement for IA's Logix V21+ driver and its Omron NJ/NX driver. It does work with older Logix processors, and also works with Rockwell's MicroLogix 8xx family (ethernet…

{ /shameless plug }

However, this:

> [@Stephen\_Smith](#):
>
> the clients "freeze" and must be re-started at least daily

Sounds like a memory leak or badly-behaved foreground script in a Vision client. That is much more trouble to find and fix--possibly requiring some redesign.