# Ignition Edge Delay

**URL:** <https://forum.inductiveautomation.com/t/ignition-edge-delay/91879>\
**Category:** Ignition\
**Tags:** vision\
**Created:** [June 14, 2024, 3:48pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-delay/91879 "2024-06-14T15:48:54Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![jacob.ramirez](https://avatars.discourse-cdn.com/v4/letter/j/9dc877/32.png) [@jacob.ramirez](https://forum.inductiveautomation.com/u/jacob.ramirez)\
**Post date:** [June 14, 2024, 3:48pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-delay/91879/1 "2024-06-14T15:48:54Z")

</div>

Has anyone had an issue with data not updating on a Vision client as fast as it transmits via MQTT?

I have gotten some feedback from users in the field that the local Panel PC on the equipment doesn't update as fast as the Ignition gateway in the cloud. The data is transmitted from the same Panel PC that's running the vision client.

Curious if anyone else has had this same issue. I have not noticed it myself yet though.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 14, 2024, 3:52pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-delay/91879/2 "2024-06-14T15:52:23Z")

</div>

Have you configured the project's poll rate? The default is 250ms. Tag updates faster than the poll rate will be merged.

---

<div class="post-metadata">

**Author:** ![jacob.ramirez](https://avatars.discourse-cdn.com/v4/letter/j/9dc877/32.png) [@jacob.ramirez](https://forum.inductiveautomation.com/u/jacob.ramirez)\
**Post date:** [June 14, 2024, 3:54pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-delay/91879/3 "2024-06-14T15:54:58Z")

</div>

The Project -\> General -\> Tag Settings -\> Client Poll Rate is set to 250.