As currently implemented:  
No later than every 60 seconds, the edge historian runs a maintenance task that finds the _oldest_ timestamp in the historian, and then deletes all data older than (not equal to) that timestamp.

There is no logic I can see to evict new incoming data eagerly, so you absolutely could exceed the row "limit" for some period of time until records are evicted.

The `tags.history.InternalHistorian.Engine` logger on debug or trace would be informative to follow, OP.

---