# Ignition edge OPC - UA faulted

**URL:** <https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102>\
**Category:** Ignition\
**Tags:** ignition80\
**Created:** [February 7, 2021, 11:18am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102 "2021-02-07T11:18:26Z")\
**Posts on this page:** 17\
**Page:** 1

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 11:18am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/1 "2021-02-07T11:18:27Z")

</div>

Hi,  
I have configured OPC-UA by using Ignition edge. I am getting tags from Codesys (OPTO 22 Controller) Groov Epic PR1. After sometime OPC-UA server is going to faulted automatically and it is not re-connecting again. I have tried maximum ways for fix this issue, but i can’t able to fix this…

 ![1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/4/747b485735a71c513ab39cede59c40c230202469.png)  
Please let me if have any solution for this…!!

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 7, 2021, 11:21am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/2 "2021-02-07T11:21:26Z")

</div>

Check the logs (post here, using pre-formatted option).

I will boot one of my Groovs’ later and try and help more.

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 11:28am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/3 "2021-02-07T11:28:23Z")

</div>

![OPC](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/d/bd63fbec31e0314702546533cee7f99be864b7f8.png) ![OPC1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/8/880deeee9d4848a641c7f62925127232f85457f9.png) ![OPC2](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/3/83fd364e279dc254324307d8d49be3924f91e596.png) ![OPC3](https://us1.discourse-cdn.com/inductiveautomation/original/3X/9/8/98cd6572e852afdfd5409da9096c1ba064b03b8a.png) ![GV1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/d/2ddcd6a61e335d7601843838ef4ed18b36b3798b.png) ![GV2](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/5/251934f0cfbb9a1ac255c2442b56e852b13fccd3.png)

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 7, 2021, 11:29am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/4 "2021-02-07T11:29:59Z")

</div>

Go to status/logs and type “OPC” into the filter.

Copy and paste the text here using the preformatted button (it looks like this \</\>) in the menu above where you type.

And welcome to the community!

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 7, 2021, 11:31am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/5 "2021-02-07T11:31:29Z")

</div>

Also, is this a one box solution?

Groov is running Edge within the PAC?

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 11:35am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/6 "2021-02-07T11:35:25Z")

</div>

Not PAC, Groov is running in CODESYS Controller

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 7, 2021, 11:37am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/7 "2021-02-07T11:37:46Z")

</div>

Groov (EPIC) is a product name, a description of a hardware Programmable Automation Controller. PAC Control is an IDE that uses OptoScript.

**Where is Edge running** , internally on the Groov hardware or on a separate IPC?

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 11:46am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/8 "2021-02-07T11:46:16Z")

</div>

Edge is running on the groov hardware

 ![1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/2/c2e478d20616705b43998ca27ca66041c906c4f2.png) ![2](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/0/50e46514de7c1c17f28c40bed6e11ce785df8561.png)

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 11:50am UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/9 "2021-02-07T11:50:06Z")

</div>

Just now again Ignition edge gone to fault mode, This is latest Log file while get faulted

```auto
UascClientMessageHandler	07Feb2021 17:25:20	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:25:04	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:24:48	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:24:40	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 17:24:36	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
SessionFsm	07Feb2021 17:24:03	[8] Keep Alive failureCount=2 exceeds failuresAllowed=1
UascClientMessageHandler	07Feb2021 16:04:35	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:04:19	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:04:03	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:03:47	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:03:31	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:03:15	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:59	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:43	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:27	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:02:11	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:55	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:39	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:23	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:01:07	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:51	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:35	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:19	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 16:00:03	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:59:47	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:59:31	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:59:15	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:59	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:43	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:26	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:58:10	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:54	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:38	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:22	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:57:06	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:50	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:34	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:18	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:56:02	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:55:46	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:55:30	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:55:14	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:58	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:42	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:26	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:54:10	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:54	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:38	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:22	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:53:06	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:50	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:34	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:18	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:52:02	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:51:46	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:51:30	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:51:14	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:58	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:42	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:26	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:50:10	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:54	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:38	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:22	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:49:06	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:50	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:34	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:18	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:48:02	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:47:46	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:47:30	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:47:14	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:57	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:41	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:25	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:46:09	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:53	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:37	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:21	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:45:05	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:44:49	[remote=localhost/127.0.0.1:4840] errorMessage=ErrorMessage{error=StatusCode{name=Bad_ServiceUnsupported, value=0x800B0000, quality=bad}, reason=null}
UascClientMessageHandler	07Feb2021 15:44:33	

```

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 7, 2021, 1:41pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/10 "2021-02-07T13:41:04Z")

</div>

Did you follow Opto University for setup?

I’ll be honest, I don’t use CoDeSys version.

You might get a faster reply here: [https://forums.opto22.com/](https://forums.opto22.com/)

Or maybe @Kevin.Herron can advise what logs to change to trace to narrow it down.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2021, 1:51pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/11 "2021-02-07T13:51:19Z")

</div>

This is a bug in codesys servers that we’ve implemented a workaround for in 8.1.1 or 8.1.2.

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 1:51pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/12 "2021-02-07T13:51:59Z")

</div>

Thank you…!!

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 1:52pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/13 "2021-02-07T13:52:39Z")

</div>

Is there any alternative solution?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2021, 1:53pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/14 "2021-02-07T13:53:19Z")

</div>

Upgrade to a version of codesys that fixes it, if there is one.

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [February 7, 2021, 1:56pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/15 "2021-02-07T13:56:34Z")

</div>

Or change to PAC control within the EPIC.

---

<div class="post-metadata">

**Author:** ![projects3](https://avatars.discourse-cdn.com/v4/letter/p/f19dbf/32.png) [@projects3](https://forum.inductiveautomation.com/u/projects3)\
**Post date:** [February 7, 2021, 2:18pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/16 "2021-02-07T14:18:02Z")

</div>

Ok…

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2021, 2:20pm UTC](https://forum.inductiveautomation.com/t/ignition-edge-opc-ua-faulted/43102/17 "2021-02-07T14:20:12Z")

</div>

I checked release notes, it should be fixed in 8.1.1 or later:

> Implemented workaround for reconnecting to servers that don't respond correctly to subscription transfer requests.