# Ignition & Logix Best Practice Tips for better communications

**URL:** <https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386>\
**Category:** Ignition\
**Tags:** rockwell\
**Created:** [June 5, 2022, 11:46pm UTC](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386 "2022-06-05T23:46:38Z")\
**Posts on this page:** 1\
**Showing post:** 52

<div class="post-metadata">

**Author:** ![nminchin](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nminchin/32/6911_2.png) [@nminchin](https://forum.inductiveautomation.com/u/nminchin)\
**Post date:** [April 25, 2025, 9:59pm UTC](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386/52 "2025-04-25T21:59:49Z")

</div>

> [@Kevin.Herron](#):
>
> CIP Connection Size from 500 to 4000

I always forget about this...

Holy moly

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/7/8762134e0c697be07479a5cbfa1b35889a9e0d60.png)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/9/19046f2f4bf97e071371e41a199c2130412c51fe.png)

Edit:  
Updated results with tests using different CIP Connection sizes:

| Test | Ext Access | CIP Connection Size | Tag Count | Requested Sample Rate (ms) | Actual Sample Rate (ms) | Request Count | Overload |
| --- | --- | --- | --- | --- | --- | --- | --- |
| UDTs | All Read/Write | 500 | 6787 | 10 | _45.48_ | 14 | _355%_ |
| UDTs | All Read/Write | 4000 | 6787 | 10 | 10.06 | 2 | 1% |
| AOI Local Tags (UDT) | All Read/Write | 500 | 6787 | 10 | _50.86_ | 14 | _409%_ |
| AOI Local Tags (UDT) | All Read/Write | 4000 | 6787 | 10 | 10.08 | 2 | 1% |
| AOI Parameter Tags | All Read/Write except EnableIn/Out | 4000 | 6787 | 10 | _ **519.02** _ | 33 | _ **5090%** _ |
| Aliased UDT Array Elements | All Read/Write | 4000 | 6760 | 10 | 10.06 | 2 | 1% |
| UDT Array Elements | All Read/Write | 4000 | 6787 | 10 | 10.06 | 2 | 1% |

---

_[View the full topic](https://forum.inductiveautomation.com/t/ignition-logix-best-practice-tips-for-better-communications/60386)._