# Ignition OPC Client open Two Session connection to PLC Siemens 1500

**URL:** <https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [February 7, 2024, 10:32pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412 "2024-02-07T22:32:19Z")\
**Posts on this page:** 9\
**Page:** 1

<div class="post-metadata">

**Author:** ![Yousef\_Ali](https://avatars.discourse-cdn.com/v4/letter/y/87869e/32.png) [@Yousef\_Ali](https://forum.inductiveautomation.com/u/Yousef_Ali)\
**Post date:** [February 7, 2024, 10:32pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/1 "2024-02-07T22:32:19Z")

</div>

Hi @Kevin.Herron I have different PLCs S7-1500 connected to Ignition Gateway , i noticed Ignition GW one PLC opens two sessions of connection to PLC . i delete the connection twice and still same issue . Both session getting same EndpointUrl came from same Server with same name only the last numbers are different as showing in snapshoot  
Rest of PLC is working fine, Only one session per PLC connection .  
This cause issue in data quality as some of these data showing bad quality with error  
`Bad_TooManyMonitoredItems: The request could not be processed because there are too many monitored items in the subscription.`

any guidance for troubleshooting

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/b/3/b3a9f28bd88ca8d4b2311bac4ecb771bef8c59be.png)

Noticed also both sessions had same applicationuri

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/6/56ca1600c75f269a6323991c022e4903cdcf8dd0.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2024, 10:42pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/2 "2024-02-07T22:42:59Z")

</div>

Disable the connection and see if both sessions disappear. You can use UaExpert to view that server's diagnostics.

Make sure you don't have another Ignition gateway that's e.g. running a backup of this one that is also making a connection.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2024, 10:45pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/3 "2024-02-07T22:45:42Z")

</div>

BTW, those numbers Ignition uses in the session name are timestamps.

In your case, one session is significantly older:

```auto
jshell> new Date(1707217324900L)
$1 ==> Tue Feb 06 03:02:04 PST 2024

jshell> new Date(1707344060550L)
$2 ==> Wed Feb 07 14:14:20 PST 2024

```

---

<div class="post-metadata">

**Author:** ![Yousef\_Ali](https://avatars.discourse-cdn.com/v4/letter/y/87869e/32.png) [@Yousef\_Ali](https://forum.inductiveautomation.com/u/Yousef_Ali)\
**Post date:** [February 7, 2024, 10:55pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/4 "2024-02-07T22:55:29Z")

</div>

Disable connection from Gateway . one session disappeared and other session sttil valid  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/6/f678c92f5eb485c5f3093a2b6db84485bc558421.png)

```auto
jshell> new Date(1707217324900L)
$1 ==> Tue Feb 06 03:02:04 PST 2024

```

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2024, 10:56pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/5 "2024-02-07T22:56:39Z")

</div>

Is there another Gateway running? Is this part of a redundant pair?

---

<div class="post-metadata">

**Author:** ![Yousef\_Ali](https://avatars.discourse-cdn.com/v4/letter/y/87869e/32.png) [@Yousef\_Ali](https://forum.inductiveautomation.com/u/Yousef_Ali)\
**Post date:** [February 7, 2024, 10:59pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/6 "2024-02-07T22:59:46Z")

</div>

i was part of a Redundant but now main gateway running as an independent Gateway . Rest of PLC was connected as well before

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 7, 2024, 11:01pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/7 "2024-02-07T23:01:43Z")

</div>

If the backup gateway is still running then it would have a connection.

The default session lifetime is only 2 minutes. There's either a bug causing an orphaned session or there's another Ignition gateway connected to it.

If you shut down this gateway you know about and the other session doesn't disappear after a couple minutes (at most), then you definitely have another gateway running.

---

<div class="post-metadata">

**Author:** ![Yousef\_Ali](https://avatars.discourse-cdn.com/v4/letter/y/87869e/32.png) [@Yousef\_Ali](https://forum.inductiveautomation.com/u/Yousef_Ali)\
**Post date:** [February 7, 2024, 11:03pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/8 "2024-02-07T23:03:01Z")

</div>

Thanks, Kevin , i will update the outcome once back to IT team .

---

<div class="post-metadata">

**Author:** ![Yousef\_Ali](https://avatars.discourse-cdn.com/v4/letter/y/87869e/32.png) [@Yousef\_Ali](https://forum.inductiveautomation.com/u/Yousef_Ali)\
**Post date:** [February 8, 2024, 3:19pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-client-open-two-session-connection-to-plc-siemens-1500/85412/9 "2024-02-08T15:19:02Z")

</div>

This PLC add in redundant server by mistake. Thanks @Kevin.Herron