# Ignition OPC UA Connection to UaExpert OPC Client is not working

**URL:** <https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [July 26, 2022, 8:36pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322 "2022-07-26T20:36:16Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![nirav.t.patel](https://avatars.discourse-cdn.com/v4/letter/n/839c29/32.png) [@nirav.t.patel](https://forum.inductiveautomation.com/u/nirav.t.patel)\
**Post date:** [July 26, 2022, 8:36pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322/1 "2022-07-26T20:36:16Z")

</div>

I am trying to connect and consume data from the Ignition OPC UA server.

I have following settings:  
Bind Port: 62541  
Bind Address: localhost  
End Point Address: 192.168.68.67 (This is the machine with Ignition)  
Security: None,Basic128Rsa15,Basic256Sha256

User source: opcua-module (default)

Now on the UaExpert (latest version) machine (192.168.68.69)  
In the custom discovery I have following: opc.tcp://192.168.68.67:62541/discovery  
After select discover nothing is happening.

Not sure what is wrong! Any help will be appreciated.  
Thanks

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 26, 2022, 8:43pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322/2 "2022-07-26T20:43:59Z")

</div>

If UaExpert is on another machine you need to set the bind address to something like `0.0.0.0` and restart the server for it to take effect.

---

<div class="post-metadata">

**Author:** ![nirav.t.patel](https://avatars.discourse-cdn.com/v4/letter/n/839c29/32.png) [@nirav.t.patel](https://forum.inductiveautomation.com/u/nirav.t.patel)\
**Post date:** [July 26, 2022, 9:14pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322/3 "2022-07-26T21:14:47Z")

</div>

I changed the bind address to 0.0.0.0 and restart OPC UA module and as well the ignition server. But still no luck with connection.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 26, 2022, 9:15pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322/4 "2022-07-26T21:15:40Z")

</div>

You might also need to open firewall ports on your server.

---

<div class="post-metadata">

**Author:** ![nirav.t.patel](https://avatars.discourse-cdn.com/v4/letter/n/839c29/32.png) [@nirav.t.patel](https://forum.inductiveautomation.com/u/nirav.t.patel)\
**Post date:** [July 26, 2022, 11:06pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322/5 "2022-07-26T23:06:26Z")

</div>

Thanks @pturmel and @Kevin.Herron. So applying inbound firewall rule and bind address did the trick.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [June 26, 2025, 3:54pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-connection-to-uaexpert-opc-client-is-not-working/62322/6 "2025-06-26T15:54:21Z")

</div>

7 posts were split to a new topic: [Error connecting to OPC Expert server](https://forum.inductiveautomation.com/t/error-connecting-to-opc-expert-server/107845)