# Ignition OPC UA Server	OPC UA	Unknown	FAULTED

**URL:** <https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464>\
**Category:** Ignition\
**Created:** [October 7, 2020, 3:58pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464 "2020-10-07T15:58:08Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 3:58pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/1 "2020-10-07T15:58:08Z")

</div>

I recently installed Ignition version: **8.1.0-rc1 (b2020091420)**. On starting it I get OPC UA server fault: **Ignition OPC UA Server OPC UA Unknown FAULTED**. The error is pasted below:

UaException: status=Bad\_ConfigurationError, message=no matching endpoints found  
at com.inductiveautomation.ignition.gateway.opcua.client.ManagedClientKt.initialize(ManagedClient.kt:127)  
at com.inductiveautomation.ignition.gateway.opcua.client.ManagedClientKt$initialize$1.invokeSuspend(ManagedClient.kt)  
at kotlin.coroutines.jvm.internal.BaseContinuationImpl.resumeWith(ContinuationImpl.kt:33)  
at kotlinx.coroutines.DispatchedTask.run(DispatchedTask.kt:56)  
at kotlinx.coroutines.scheduling.CoroutineScheduler.runSafely(CoroutineScheduler.kt:571)  
at kotlinx.coroutines.scheduling.CoroutineScheduler$Worker.executeTask(CoroutineScheduler.kt:738)  
at kotlinx.coroutines.scheduling.CoroutineScheduler$Worker.runWorker(CoroutineScheduler.kt:678)  
at kotlinx.coroutines.scheduling.CoroutineScheduler$Worker.run(CoroutineScheduler.kt:665)

8.1.0-rc1 (b2020091420)  
Azul Systems, Inc. 11.0.7

How to fix this error?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 7, 2020, 4:04pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/2 "2020-10-07T16:04:54Z")

</div>

Was this an upgrade or a fresh install?

Are there any errors in your logs from the OPC UA server during startup?

You can probably fix this by going through the endpoint discovery process for that connection again, but it would be interesting to figure out how you’ve gotten here.

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 4:11pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/3 "2020-10-07T16:11:00Z")

</div>

I just upgraded the previous trial version (it was of course version 8, but don't remember exactly which version, but it was installed may be 6 months ago). I just reinstalled it on the existing version with all default options! On starting the newly installed version, I get this error! I didn't do anything special or new or different, just ran the newly installed version! It recovered all my projects and scripts fine, except for this OPC faulted error!

Of course, I had done a mistake of deleting the .idb file from the log folder, just to clear every thing in that folder. This caused the data base error as well as OPC error, but on stopping and restarting the Ignition server ,the data base error disappeared, but OPC error continued!

Do I have to try reinstalling the Ignition and try the whole process again!

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 7, 2020, 4:30pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/4 "2020-10-07T16:30:11Z")

</div>

Can you upload your logs somewhere?

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 4:36pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/5 "2020-10-07T16:36:33Z")

</div>

Unfortunately I have deleted all the logs , I think I will reinstall the ignition and generate the logs again, it may even clear this error as well!

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 5:05pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/6 "2020-10-07T17:05:21Z")

</div>

I reinstalled the whole Ignition version, but the OPC error persists! I am attaching the log file this time.[wrapper.log](https://forum.inductiveautomation.com/uploads/short-url/j6QFhRPcawWojOhWSXYTKdCO260.log) (58.8 KB)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 7, 2020, 5:11pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/7 "2020-10-07T17:11:17Z")

</div>

In the config section of the gateway, go to that connection, choose More \> Endpoint. Then click “Skip to advanced configuration” on the next page. What are those settings? Screenshot will work.

Also get a screenshot of the server settings under Config \> OPC UA \> Server Settings.

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 5:17pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/8 "2020-10-07T17:17:01Z")

</div>

Screen shot -1

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/5/65890ad6573bfb3210b9f7a27fe8af25da87d998.png)

Screen shot-2

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/a/1ac07f801c8ce8d2380e2c2d16e69059a5192f85.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 7, 2020, 5:28pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/9 "2020-10-07T17:28:18Z")

</div>

Okay, so you somehow have only “None” allowed in your Security Policies setting in the server configuration, but your connection is setup to use Basic256Sha256.

Change that to “None,Basic256Sha256” and restart.

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 5:35pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/10 "2020-10-07T17:35:39Z")

</div>

yes sir! It worked. No error now! But I don't know how it got a value only 'none'! Does the new installer have default value and 'none'? Or does it take it from previous installation configuration, where I might have changed it to 'non' (but quite unlikely that I would have changed this value!)

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/6/16e016196262588224ec735babad192a1c3ae7e8.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 7, 2020, 5:37pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/11 "2020-10-07T17:37:04Z")

</div>

> [@prafull\_j](#):
>
> Or does it take it from previous installation configuration, where I might have changed it to ‘non’ (but quite unlikely that I would have changed this value!)

Almost certainly this.

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 5:40pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/12 "2020-10-07T17:40:07Z")

</div>

May be during testing the OPC scripting functions, I might have changed it due to some error! Perhaps I must have been advised by you to do so in case of failure of some function!

Thanks , you are a true expert on Ignition's OPC UA server!

---

<div class="post-metadata">

**Author:** ![PRAMANJ](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pramanj/32/66935_2.png) [@PRAMANJ](https://forum.inductiveautomation.com/u/PRAMANJ)\
**Post date:** [October 7, 2020, 6:01pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-opc-ua-unknown-faulted/39464/13 "2020-10-07T18:01:29Z")

</div>

Yes while testing external OPC UA client accessing Ignition OPC UA server, I had changed the security settings to 'None' and forgot to change back to 'None,Basic256Sha256'  
see post 24 onwards in [system.opc.readValue config error - #29 by prafull\_j](http://forum.inductiveautomation.com/t/system-opc-readvalue-config-error/34916/29)