# Ignition OPC UA Server Redundancy (Modbus TCP)

**URL:** <https://forum.inductiveautomation.com/t/ignition-opc-ua-server-redundancy-modbus-tcp/67123>\
**Category:** Ignition\
**Tags:** redundancy\
**Created:** [December 1, 2022, 7:49am UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-redundancy-modbus-tcp/67123 "2022-12-01T07:49:00Z")\
**Posts on this page:** 1\
**Showing post:** 10

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 12, 2023, 4:23pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-redundancy-modbus-tcp/67123/10 "2023-07-12T16:23:12Z")

</div>

It wasn't quite as easy as the last change, but relatively easy. _ **Utterly untested** _, feedback welcome:

**BETA** for Ignition 8.1: ~~v1.1.4.231931604~~

Some notes:

- When active, the driver alternates between the live connections on a per-batch basis. For this driver, a "batch" is a memory area subset of a single `system.opc.readValues()` request, `system.opc.writeValues()` request, or subscription poll. (Coils with coils, discrete inputs with discretes, et cetera.) This is effectively load-balancing between the connections, though not deliberately so. (Batch sizes vary and are not considered in the toggling.)

- When a single connection breakage occurs, the batches that were queued to the now-broken connection will fail. For subscriptions, bad quality will appear for one subscription cycle. Non-subscription reads and any writes should be monitored for error results and retried.

- Only available for Modbus TCP, not any form of RTU.

- Device status will include "Degraded" or "Recovering" if the two connection states differ.

I probably won't have a chance to properly test this until next week. I thought y'all might like this preview.

---

_[View the full topic](https://forum.inductiveautomation.com/t/ignition-opc-ua-server-redundancy-modbus-tcp/67123)._