On what port and what driver do we connect a RedLion to Ignition OPC UA???

Port 790???  
Modbus??

Thanks

---

<div class="post-metadata">

**Author:** ![greg.simpson](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/greg.simpson/32/3135_2.png) [@greg.simpson](https://forum.inductiveautomation.com/u/greg.simpson)\
**Post date:** [May 8, 2014, 11:41pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-to-map-redlion-plc/8426/2 "2014-05-08T23:41:09Z")

</div>

If the device supports Modbus then use that driver. The port used by Modbus is 502. We would need more specific information about the PLC to answer this question.

---

<div class="post-metadata">

**Author:** ![camachom](https://avatars.discourse-cdn.com/v4/letter/c/ce7236/32.png) [@camachom](https://forum.inductiveautomation.com/u/camachom)\
**Post date:** [May 9, 2014, 12:07am UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-to-map-redlion-plc/8426/3 "2014-05-09T00:07:28Z")

</div>

Thanks Greg for yoru reply

ProducTVity Station

[redlion.net/Products/Groups/ … /07051.pdf](http://www.redlion.net/Products/Groups/ProducTVityStation/ProducTVityStation/Docs/07051.pdf)

It has a built in OPC Master, but can not connect to it

And also pull data from a RedLion G306

[redlion.net/Products/HumanMa … /G306.html](http://www.redlion.net/Products/HumanMachineInterface/OperatorInterface/G306.html)

Thanks for your suport

---

<div class="post-metadata">

**Author:** ![diat150](https://avatars.discourse-cdn.com/v4/letter/d/a587f6/32.png) [@diat150](https://forum.inductiveautomation.com/u/diat150)\
**Post date:** [May 9, 2014, 2:09am UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-to-map-redlion-plc/8426/4 "2014-05-09T02:09:54Z")

</div>

you need to use the opc-da module, not opc-ua.

---

<div class="post-metadata">

**Author:** ![greg.simpson](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/greg.simpson/32/3135_2.png) [@greg.simpson](https://forum.inductiveautomation.com/u/greg.simpson)\
**Post date:** [May 9, 2014, 8:34pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-to-map-redlion-plc/8426/5 "2014-05-09T20:34:28Z")

</div>

Using OPC-DA you may want to take a look at this article

[inductiveautomation.com/support/kb?0=152](http://inductiveautomation.com/support/kb?0=152)

---

<div class="post-metadata">

**Author:** ![camacho\_marco](https://avatars.discourse-cdn.com/v4/letter/c/49beb7/32.png) [@camacho\_marco](https://forum.inductiveautomation.com/u/camacho_marco)\
**Post date:** [May 28, 2014, 5:33pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-to-map-redlion-plc/8426/6 "2014-05-28T17:33:16Z")

</div>

Thanks Greg for your information. Will follow up on your recommendations

Cheers