Does anyone know if Ignition OPC-UA can be used with the GE Versamax PLC’s?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 3, 2014, 8:24pm UTC](https://forum.inductiveautomation.com/t/ignition-opc-ua-with-ge-versamax/8092/2 "2014-03-03T20:24:59Z")

</div>

We don’t have a driver for whatever the native protocol is, but if they support Modbus you can use Ignition’s Modbus driver.

Otherwise you can use another OPC server (Kepware, maybe?) that has support for these devices and then make an OPC connection to that server.