# Ignition throwing "Error\_Configuration" when setting up Modbus tags

**URL:** <https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684>\
**Category:** Ignition\
**Created:** [March 27, 2022, 4:01pm UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684 "2022-03-27T16:01:57Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![fshriver](https://avatars.discourse-cdn.com/v4/letter/f/db5fbb/32.png) [@fshriver](https://forum.inductiveautomation.com/u/fshriver)\
**Post date:** [March 27, 2022, 4:01pm UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684/1 "2022-03-27T16:01:57Z")

</div>

I’m trying to set up Ignition to poll values from a Modbus server, but for some reason when I configure the tags in Designer it keeps throwing “Error\_Configuration” and returning “Error\_Configuration(“Bad\_NodeIdUnknown: The node id refers to a node that does not exist in the server address space.”)” for the Quality indicator. I’m confused, however, because I’ve done exactly this process already in Ignition Edge and had no issues. I even cloned the JSON tag definitions from the successful Ignition Edge install and pasted them into this new project, but still no luck. And the Ignition Gateway doesn’t appear to be having any issues connecting to the Modbus server itself.

Here’s a screenshot of the error screen I see in Designer:

 ![ignition_problem_p1](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/3/e36b48598cb00a5c077a73ef405257049eadb7a4.png)

Here’s a screenshot of the gateway status for the relevant Modbus device:

 ![ignition_problem_p2](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/5/3523be2cffbed892bf10ca93ba83c2c7b13d764f.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 27, 2022, 7:29pm UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684/2 "2022-03-27T19:29:03Z")

</div>

Weird. Any accidental spaces in or at the end of the device name or OPC Item Path?

Is the endpoint URL for the “Ignition OPC UA Server” connection definitely pointed at localhost and not some other server that doesn’t have this device configured?

---

<div class="post-metadata">

**Author:** ![Harry\_Lodge](https://avatars.discourse-cdn.com/v4/letter/h/d2c977/32.png) [@Harry\_Lodge](https://forum.inductiveautomation.com/u/Harry_Lodge)\
**Post date:** [April 14, 2022, 12:28am UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684/3 "2022-04-14T00:28:01Z")

</div>

This may seem like a weird question but have you tried setting the OpcItemPath one by one?

I’m getting a similar issue that happens if i attempt to set multiple tags at once. This happens even when the path is correct and predefined in the UDT.

---

<div class="post-metadata">

**Author:** ![AJBerera](https://avatars.discourse-cdn.com/v4/letter/a/9fc29f/32.png) [@AJBerera](https://forum.inductiveautomation.com/u/AJBerera)\
**Post date:** [August 31, 2022, 12:47pm UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684/4 "2022-08-31T12:47:03Z")

</div>

I am also seeing this on a chart recorder I am attempting to connect to with modbus TCP, the instrument also shows as being connected in devices page.

I have tried many variations of registers from the HA028910ENG\_16\_6100A\_6180A\_Graphic\_Recorder\_User\_Guide

Integer  
Ignition OPC-UA Server  
Address like [Boiler]1.951

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [August 31, 2022, 1:03pm UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684/5 "2022-08-31T13:03:19Z")

</div>

> [@AJBerera](#):
>
> [Boiler]1.951

That's not a valid Modbus address for Ignition's driver.

[https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing](https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing)

---

<div class="post-metadata">

**Author:** ![AJBerera](https://avatars.discourse-cdn.com/v4/letter/a/9fc29f/32.png) [@AJBerera](https://forum.inductiveautomation.com/u/AJBerera)\
**Post date:** [September 9, 2022, 2:41pm UTC](https://forum.inductiveautomation.com/t/ignition-throwing-error-configuration-when-setting-up-modbus-tags/57684/6 "2022-09-09T14:41:44Z")

</div>

I found the correct addresses. No problems now.