# Ignition to EtherNet/IP without a PLC

**URL:** <https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536>\
**Category:** Ignition\
**Created:** [July 13, 2019, 1:24am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536 "2019-07-13T01:24:33Z")\
**Posts on this page:** 20\
**Page:** 1

<div class="post-metadata">

**Author:** ![rzrbacks](https://avatars.discourse-cdn.com/v4/letter/r/6bbea6/32.png) [@rzrbacks](https://forum.inductiveautomation.com/u/rzrbacks)\
**Post date:** [July 13, 2019, 1:24am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/1 "2019-07-13T01:24:33Z")

</div>

Is it possible for Ignition to talk directly to a device that talks EtherNet/IP without a PLC in between? Kepware or some other software/hardware?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 13, 2019, 1:49am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/2 "2019-07-13T01:49:35Z")

</div>

That sounds interesting…

[Ethernet/IP Class 1 Communications](https://inductiveautomation.com/moduleshowcase/module/automation-professionals-llc-ethernetip-class-1-communications)

(:

---

<div class="post-metadata">

**Author:** ![rzrbacks](https://avatars.discourse-cdn.com/v4/letter/r/6bbea6/32.png) [@rzrbacks](https://forum.inductiveautomation.com/u/rzrbacks)\
**Post date:** [July 13, 2019, 2:40am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/3 "2019-07-13T02:40:19Z")

</div>

I looked at the module you posted and it still looks like it would require a PLC between Ignition and my end devices. Is that the case? We want to avoid putting a PLC on the floor that is just there for communication purposes. Thanks!

---

<div class="post-metadata">

**Author:** ![jlivingston](https://avatars.discourse-cdn.com/v4/letter/j/779978/32.png) [@jlivingston](https://forum.inductiveautomation.com/u/jlivingston)\
**Post date:** [July 13, 2019, 3:59am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/4 "2019-07-13T03:59:25Z")

</div>

Regarding the …“It still looks like it would require a PLC”… See Documentation:

[https://www.automation-pros.com/enip1/UserManual.pdf](https://www.automation-pros.com/enip1/UserManual.pdf) which was part of what Mr. Turmel was trying to tell you. There are devices other than Rockwell Automation ( eg. ProSoft makes modules compatible with RA PLCs that do not need to be mechanically connected to the PLC ), but without knowing what you want to connect- the question is probably one that you can not get an easy answer for. There are all sorts of modules available for different types of communication that may be installed on an Ignition server. When you specify EtherNet/IP rather than Ethernet over a particular type of path such as IEEE 802.3i or 802.3j it might be better if you could spell out TCP (Y/N) UDP or IP or other tunnel protocol eg. TN3270 session over 10BASE-F. As Mr. Turmel would remind me, there is a support portion to be considered, the link similar to [https://support.inductiveautomation.com](https://support.inductiveautomation.com) yet you may want to look at the policy section there before calling the voice number. Please post your results here, there are always folks who want to know how you succeed or not.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 13, 2019, 4:23pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/5 "2019-07-13T16:23:23Z")

</div>

> [@rzrbacks](#):
>
> require a PLC between Ignition and my end devices.

Without the scanner option, it is an I/O slave and a target for other PLCs' message instructions.

With the scanner option, it is also an I/O master -- _ **no PLC required** _.

In case it isn't clear from my profile, I'm the author of this module.

---

<div class="post-metadata">

**Author:** ![laura.strydom](https://avatars.discourse-cdn.com/v4/letter/l/3da27b/32.png) [@laura.strydom](https://forum.inductiveautomation.com/u/laura.strydom)\
**Post date:** [December 11, 2023, 7:14am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/6 "2023-12-11T07:14:10Z")

</div>

Hi @pturmel,

I see that under your module on the IA website the 8.1 platform isn't listed.  
Does it, by any chance, support 8.1?

---

<div class="post-metadata">

**Author:** ![Matrix\_Engineering](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/matrix_engineering/32/19781_2.png) [@Matrix\_Engineering](https://forum.inductiveautomation.com/u/Matrix_Engineering)\
**Post date:** [December 11, 2023, 8:39am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/7 "2023-12-11T08:39:02Z")

</div>

It has a different name now

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190):
>
> Automation Professionals is pleased to announce its latest EtherNet/IP Communications Suite driver module, a major upgrade to its EtherNet/IP Class1 Communications module, as a Public Beta. As of April 15, 2023, this is now a Production Release. The primary new feature is its new Generic EtherNet/IP Client Driver, a drop-in replacement for IA's Logix V21+ driver and its Omron NJ/NX driver. It does work with older Logix processors, and also works with Rockwell's MicroLogix 8xx family (ethernet…

---

<div class="post-metadata">

**Author:** ![laura.strydom](https://avatars.discourse-cdn.com/v4/letter/l/3da27b/32.png) [@laura.strydom](https://forum.inductiveautomation.com/u/laura.strydom)\
**Post date:** [December 11, 2023, 10:09am UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/8 "2023-12-11T10:09:53Z")

</div>

Thank you!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [December 11, 2023, 1:03pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/9 "2023-12-11T13:03:06Z")

</div>

> [@laura.strydom](#):
>
> isn't listed.

It is listed in IA's [Module Showcase](https://inductiveautomation.com/moduleshowcase/). The main link to that has moved around on IA's website at various times--it is now in the lower right corner of the "Product" menu of the main site.

---

<div class="post-metadata">

**Author:** ![Matthew\_DeLuca](https://avatars.discourse-cdn.com/v4/letter/m/3ab097/32.png) [@Matthew\_DeLuca](https://forum.inductiveautomation.com/u/Matthew_DeLuca)\
**Post date:** [September 11, 2024, 7:08pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/10 "2024-09-11T19:08:53Z")

</div>

Has this ever been proven to work with Universal Robots?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 11, 2024, 7:13pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/11 "2024-09-11T19:13:01Z")

</div>

I have not used those myself. If you get me the EDS file, I'll evaluate it for you.

---

<div class="post-metadata">

**Author:** ![Matthew\_DeLuca](https://avatars.discourse-cdn.com/v4/letter/m/3ab097/32.png) [@Matthew\_DeLuca](https://forum.inductiveautomation.com/u/Matthew_DeLuca)\
**Post date:** [September 11, 2024, 7:51pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/12 "2024-09-11T19:51:36Z")

</div>

I am not able to upload the eds file. A download link can be found at the bottom of the page.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/7/c70556231bbaa78476a59f0e2ddf6098e902a498.png)

---

<div class="post-metadata">

**Author:** ![keari0913](https://avatars.discourse-cdn.com/v4/letter/k/c77e96/32.png) [@keari0913](https://forum.inductiveautomation.com/u/keari0913)\
**Post date:** [September 11, 2024, 8:04pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/13 "2024-09-11T20:04:01Z")

</div>

Has this ever worked with Kaeser Compressor's SAM controller Ethernet/IP comms module?  
What would be the best way to get an EDS file to you?

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [September 11, 2024, 8:16pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/14 "2024-09-11T20:16:55Z")

</div>

Screenshots of links are unusable. Is this the link you're referring to:  
[https://www.universal-robots.com/articles/ur/interface-communication/ethernet-ip-guide/](https://www.universal-robots.com/articles/ur/interface-communication/ethernet-ip-guide/)

If so, this is the EDS file link for @pturmel: [https://s3-eu-west-1.amazonaws.com/ur-support-site/18712/UniversalRobot.eds](https://s3-eu-west-1.amazonaws.com/ur-support-site/18712/UniversalRobot.eds)

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 11, 2024, 8:18pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/15 "2024-09-11T20:18:10Z")

</div>

Send an email to my [Support Email](mailto:support@automation-pros.com) address. With resources attached.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 11, 2024, 8:24pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/16 "2024-09-11T20:24:50Z")

</div>

I would expect the Universal Robot to work just fine with my Scanner option. I've put together a sample XML config here:

[https://www.automation-pros.com/enip1/UniversalRobot%20AS%20Sample.xml](https://www.automation-pros.com/enip1/UniversalRobot%20AS%20Sample.xml)

Deployment notes:

- This robot uses multicast packets. Ignition **must** have a network interface in the same subnet as the robot. No routing or NATing at all.

- The IP address on Ignition's network interface in that subnet must be configured as the "Local Address" of the EtherNet/IP Host device.

- The IP address in the XML, "10.20.30.40", needs to be replaced with the real IP address of the robot.

- This configuration assumes you will command the robot from Ignition. If you wish to simply _monitor_ the robot, the scanner module config in the XML must be changed to the "Listen Only" connection type.

- The XML has the RPI set to 100ms. If you need to go faster you must carefully adjust the Garbage Collector settings in `ignition.conf`, and carefully test for GC stalls.

---

<div class="post-metadata">

**Author:** ![Matthew\_DeLuca](https://avatars.discourse-cdn.com/v4/letter/m/3ab097/32.png) [@Matthew\_DeLuca](https://forum.inductiveautomation.com/u/Matthew_DeLuca)\
**Post date:** [September 12, 2024, 1:03pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/17 "2024-09-12T13:03:53Z")

</div>

Thanks for getting the links, I had forgotten to include that as well. These are the ones I was looking at though.

---

<div class="post-metadata">

**Author:** ![lrose](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lrose/32/62724_2.png) [@lrose](https://forum.inductiveautomation.com/u/lrose)\
**Post date:** [September 12, 2024, 2:52pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/18 "2024-09-12T14:52:52Z")

</div>

> [@pturmel](#):
>
> This robot uses multicast packets. Ignition **must** have a network interface in the same subnet as the robot. No routing or NATing at all.

Is this true of any device that uses multicast packets? Is it a network rule, and Ignition thing, or somehow specific to your module and this application? Just curious.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [September 12, 2024, 3:17pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/19 "2024-09-12T15:17:10Z")

</div>

It is common for multicast packets, in general, to be sent with hop limit aka "Time To Live"== 1, limiting to one subnet. The EtherNet/IP Specification Volume 2 §3-5.2 **requires** TTL=1 by default, and when non-configurable. So, same subnet only.

Rockwell devices do not permit TTL configuration, that I've seen. Nor have I seen it on any other brands with EtherNet/IP capability. And I don't support configuring it in my module, either.

For all practical purposes in the EtherNet/IP world, multicast == same subnet.

I imagine that global media content distribution systems are the only significant users of multi-hop multicast.

---

<div class="post-metadata">

**Author:** ![Kevin\_Ortega](https://avatars.discourse-cdn.com/v4/letter/k/c67d28/32.png) [@Kevin\_Ortega](https://forum.inductiveautomation.com/u/Kevin_Ortega)\
**Post date:** [April 9, 2025, 9:13pm UTC](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536/20 "2025-04-09T21:13:31Z")

</div>

Does the Ethernet/IP Communication Suite V2 work for devices running Ignition Edge?

[Next page](https://forum.inductiveautomation.com/t/ignition-to-ethernet-ip-without-a-plc/26536.md?page=2)