# Ingnition connected with ControlLogix V32

**URL:** <https://forum.inductiveautomation.com/t/ingnition-connected-with-controllogix-v32/32297>\
**Category:** Ignition\
**Created:** [February 14, 2020, 10:12pm UTC](https://forum.inductiveautomation.com/t/ingnition-connected-with-controllogix-v32/32297 "2020-02-14T22:12:57Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![andrespumacayogomez](https://avatars.discourse-cdn.com/v4/letter/a/839c29/32.png) [@andrespumacayogomez](https://forum.inductiveautomation.com/u/andrespumacayogomez)\
**Post date:** [February 14, 2020, 10:12pm UTC](https://forum.inductiveautomation.com/t/ingnition-connected-with-controllogix-v32/32297/1 "2020-02-14T22:12:57Z")

</div>

Hi everybody,  
I have to connect a ControlLogix Revision 32 with the ignition V7.9.10, i used the OPC UA server in the gateway page. My problem, I configured all the features in the page, and at moment when i go to the ignition designer, i cannot see the tags, i tried to see the tags in the page with the quick client, and dont appear the global tags from the PLC. If someone have the samme problem or similar, i would like to know how to see the tags to drag to the ignition designer.  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/b/b894b16e66b88121106dae4df3d7c381f63082f5.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [February 14, 2020, 10:33pm UTC](https://forum.inductiveautomation.com/t/ingnition-connected-with-controllogix-v32/32297/2 "2020-02-14T22:33:09Z")

</div>

Looks like you set up the device connection with the legacy driver instead of the one that is for v21+ firmware revisions.

---

<div class="post-metadata">

**Author:** ![witman](https://avatars.discourse-cdn.com/v4/letter/w/d2c977/32.png) [@witman](https://forum.inductiveautomation.com/u/witman)\
**Post date:** [February 14, 2020, 11:47pm UTC](https://forum.inductiveautomation.com/t/ingnition-connected-with-controllogix-v32/32297/3 "2020-02-14T23:47:00Z")

</div>

As @Kevin.Herron notes, are you using this driver?

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/2X/a/ab5bcc211f460c457e7b8babf85269c3a78e54f3.png)