# Is it possible to connect Beijer Panel OPC to Ignition?

**URL:** <https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683>\
**Category:** Ignition\
**Created:** [April 29, 2025, 1:50pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683 "2025-04-29T13:50:06Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![Philip\_Svensson](https://avatars.discourse-cdn.com/v4/letter/p/ba8739/32.png) [@Philip\_Svensson](https://forum.inductiveautomation.com/u/Philip_Svensson)\
**Post date:** [April 29, 2025, 1:50pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/1 "2025-04-29T13:50:06Z")

</div>

Hello, i have a Beijer panel which i run a OPC UA server on and i was wondering if it's possible to connect it to Ignition? I have tried to connect it myself but to no success.

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [April 29, 2025, 3:12pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/2 "2025-04-29T15:12:12Z")

</div>

> I have tried to connect it myself ...

How?

> ... but to no success.

What errors did you receive?

---

<div class="post-metadata">

**Author:** ![Philip\_Svensson](https://avatars.discourse-cdn.com/v4/letter/p/ba8739/32.png) [@Philip\_Svensson](https://forum.inductiveautomation.com/u/Philip_Svensson)\
**Post date:** [April 30, 2025, 5:57am UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/3 "2025-04-30T05:57:51Z")

</div>

Hi i've tried turning OPC UA server on at the panel with ix Developer and then tried to find it using the ip and port on ignition but i get timeout error.

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [April 30, 2025, 10:07am UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/4 "2025-04-30T10:07:52Z")

</div>

If you are only going to bother writing one sentence to explain the issue, why would you expect a bunch of strangers to write anything at all to help?

If you actually want help, you are going to post screenshots of your OPC connection settings, the settings you configured in the HMI, text copies formatted correctly of the exact error messages and all the other detail you can think of to help.

---

<div class="post-metadata">

**Author:** ![Philip\_Svensson](https://avatars.discourse-cdn.com/v4/letter/p/ba8739/32.png) [@Philip\_Svensson](https://forum.inductiveautomation.com/u/Philip_Svensson)\
**Post date:** [April 30, 2025, 10:53am UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/5 "2025-04-30T10:53:55Z")

</div>

Hi, here are the screenshots. In the HMI there are not really any settings except the ip address. The HMI im using is a X2 pro 10 and im running the OPC UA server from there, and here are the configured settings from ix developer.

 ![Skärmbild 2025-04-30 124756](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/0/8049f3b348e0b9e21115b02081776e0f574c0d5c.png)

And this is the error i get when i try to find it in Ignition. I get the same error even when i try to change the ip or port and when i write /discovery at the end.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/a/5a5e07e68ced13a7505e17a872126d95f4432955.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 30, 2025, 11:49am UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/6 "2025-04-30T11:49:43Z")

</div>

Is there anything you have to do to enable it? Restart/download/etc?

Are there any firewalls that need to be turned off?

---

<div class="post-metadata">

**Author:** ![Philip\_Svensson](https://avatars.discourse-cdn.com/v4/letter/p/ba8739/32.png) [@Philip\_Svensson](https://forum.inductiveautomation.com/u/Philip_Svensson)\
**Post date:** [April 30, 2025, 12:40pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/7 "2025-04-30T12:40:18Z")

</div>

From what i understand i just need to click the "Enable OPC UA Server" and then download it to the panel and then it should run. I have'nt been able to find anything on any firewalls that need to be turned off.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [April 30, 2025, 12:53pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/8 "2025-04-30T12:53:07Z")

</div>

A "connect timeout" error like that is usually a firewall or some other network issue.

It means Ignition tries to open a TCP connection and hears _nothing_ back. Usually if the other side is reachable and e.g. the server isn't running or you have the wrong port you get a TCP RST instead, which shows up as a different error.

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [April 30, 2025, 1:20pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/9 "2025-04-30T13:20:07Z")

</div>

Is it on the same subnet as the Ignition gateway? If not you'll need to make sure both are pointing to a router that can route between the 2 subnets for their default gateways.

---

<div class="post-metadata">

**Author:** ![Philip\_Svensson](https://avatars.discourse-cdn.com/v4/letter/p/ba8739/32.png) [@Philip\_Svensson](https://forum.inductiveautomation.com/u/Philip_Svensson)\
**Post date:** [May 2, 2025, 12:00pm UTC](https://forum.inductiveautomation.com/t/is-it-possible-to-connect-beijer-panel-opc-to-ignition/105683/10 "2025-05-02T12:00:44Z")

</div>

Hi, turns out the ip i hade the gateway on the router on didn't find the panel even when they hade the same subnet and gateway. So i changed the ip of the gateway and it worked. Thanks for the help!!