# Is there a good functional reason to add two PLC connections to separate Leased and Driven tags?

**URL:** <https://forum.inductiveautomation.com/t/is-there-a-good-functional-reason-to-add-two-plc-connections-to-separate-leased-and-driven-tags/113457>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [January 21, 2026, 5:42pm UTC](https://forum.inductiveautomation.com/t/is-there-a-good-functional-reason-to-add-two-plc-connections-to-separate-leased-and-driven-tags/113457 "2026-01-21T17:42:03Z")\
**Posts on this page:** 1\
**Showing post:** 4

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [January 21, 2026, 8:38pm UTC](https://forum.inductiveautomation.com/t/is-there-a-good-functional-reason-to-add-two-plc-connections-to-separate-leased-and-driven-tags/113457/4 "2026-01-21T20:38:49Z")

</div>

> [@Kevin.Herron](#):
>
> re-optimization due to lease changes

This is not an issue with my drivers, FWIW.

The lease killer is **this** :

> [@How fast does "leased" tag time take effect](https://forum.inductiveautomation.com/t/how-fast-does-leased-tag-time-take-effect/34936/13):
>
> No, known pathological OPC client behavior. If there is any enabled OPC tag that yields unknown node, subscription changes are batched every 8 seconds.

I know Kevin plans a fix, but there no timeline that I know of.

---