I'm using the isAlarmActiveFiltered expression to determine if I have tags in alarm based on Display Name. For example, I have an expression tag called isAlarmMM01Dryer with the expression:

`isAlarmActiveFiltered("*"`_`,"*"`_`,"MM01 Dryer",1,4,0,1,0)` - Boolean, Event Driven

and it works, whether or not I have a tag with the "MM01 Dryer" display name in alarm is reflected as true or false and I have a 'Good' quality.

I made a copy of that tag and named it isAlarmMM02 and changed the expression to

`isAlarmActiveFiltered("*"`_`,"*"`_`,"MM02 Dryer",1,4,0,1,0)` and I get a quality status of "Bad\_NotFound".

I checked my Display Names and they look correct. Does the Display Name in the expression have to exist on at least one tag? I don't currently have any tags in alarm but I still get good quality on 1 and bad on 2.

---

<div class="post-metadata">

**Author:** ![JVDM](https://avatars.discourse-cdn.com/v4/letter/j/ac8455/32.png) [@JVDM](https://forum.inductiveautomation.com/u/JVDM)\
**Post date:** [May 29, 2026, 12:10pm UTC](https://forum.inductiveautomation.com/t/isalarmactive-bad-notfound-with-display-names/115756/2 "2026-05-29T12:10:20Z")

</div>

The third parameter filters for Display Path. So the first one is called `isAlarmMM01Dryer` and the second is called `isAlarmMM02`. Have you tried renaming the second one to `isAlarmMM02Dryer`? I can't guess what your entire setup looks like, but it looks odd not being an _exact_ copy (apart from the 1/2 change)

---

<div class="post-metadata">

**Author:** ![Chris\_Buehrer](https://avatars.discourse-cdn.com/v4/letter/c/9de053/32.png) [@Chris\_Buehrer](https://forum.inductiveautomation.com/u/Chris_Buehrer)\
**Post date:** [June 2, 2026, 12:26pm UTC](https://forum.inductiveautomation.com/t/isalarmactive-bad-notfound-with-display-names/115756/3 "2026-06-02T12:26:01Z")

</div>

Sorry, typo on my part. The second tag is named 'isAlarmMM02Dryer'. The expression is copy-pasted between the two, the only difference is the 1/2.

What I find odd is that it seems that even if I typed the Display Path name wrong, I would think the expression would evaluate to false. Can anyone confirm that?

Is there any way to get more detail at the OPC level of why the quality is Bad\_NotFound?

---

<div class="post-metadata">

**Author:** ![Chris\_Buehrer](https://avatars.discourse-cdn.com/v4/letter/c/9de053/32.png) [@Chris\_Buehrer](https://forum.inductiveautomation.com/u/Chris_Buehrer)\
**Post date:** [June 3, 2026, 1:59pm UTC](https://forum.inductiveautomation.com/t/isalarmactive-bad-notfound-with-display-names/115756/4 "2026-06-03T13:59:55Z")

</div>

I deleted the tag and recreated it from scratch instead of a copy/edit and it works