# Issue with reports Tag Historian Query Header on CrossTab

**URL:** <https://forum.inductiveautomation.com/t/issue-with-reports-tag-historian-query-header-on-crosstab/19434>\
**Category:** Ignition\
**Created:** [August 29, 2018, 12:21am UTC](https://forum.inductiveautomation.com/t/issue-with-reports-tag-historian-query-header-on-crosstab/19434 "2018-08-29T00:21:47Z")\
**Posts on this page:** 1\
**Page:** 1

<div class="post-metadata">

**Author:** ![PEM.Kaleo](https://avatars.discourse-cdn.com/v4/letter/p/e56c9b/32.png) [@PEM.Kaleo](https://forum.inductiveautomation.com/u/PEM.Kaleo)\
**Post date:** [August 29, 2018, 12:21am UTC](https://forum.inductiveautomation.com/t/issue-with-reports-tag-historian-query-header-on-crosstab/19434/1 "2018-08-29T00:21:47Z")

</div>

I’m using a Tag Historian Query with 8 tags as my data source to get minimum level for every day in the date range selected in a CrossTab table. Coulumn header is @tagpath@, column 1 is @Minimum@ and @t\_stamp@.

The problems is that the header is off set by one to the left. For some reason it puts “t\_stamp” in the first column header and then Well 1 in the second, Well 2 in the third and so one until the last column header is filled with the well that should be in the second to last column header.

The data and time stamps are in the correct columns and rows, only the header is offset. Any one have an idea why it’s putting the label "t\_stamp in the first column header which is causing the offset?

**Query settings**  
Date Range: Historical  
Aggregation: Minimum  
Return Format: Calculations  
Sample Size: Interval / Hour