# Issues syncing Tag History from Ignition Edge to Standard Gateway (History Sync)

**URL:** <https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532>\
**Category:** Ignition\
**Tags:** ignition83, edge\
**Created:** [May 14, 2026, 1:59pm UTC](https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532 "2026-05-14T13:59:20Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![bsantaella](https://avatars.discourse-cdn.com/v4/letter/b/7cd45c/32.png) [@bsantaella](https://forum.inductiveautomation.com/u/bsantaella)\
**Post date:** [May 14, 2026, 1:59pm UTC](https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532/1 "2026-05-14T13:59:20Z")

</div>

Hi everyone,

I'm having trouble synchronizing tag history from an **Ignition Edge (v8.3.1)** to a central **Ignition Standard Gateway**.

**Current Architecture:**

- **Edge Gateway:** Has a local historian named `edHistorian`.

- **Standard Gateway (Name: igResidual):** Has a Historian Splitter named `pgHubSpoke` (which points to a local SQL DB and a remote Hub).

- The **Gateway Network** connection is established and "Running" between both nodes.

**The Issue:** I have configured the **Edge Sync Settings** to point to the Remote Gateway `igResidual` and the Remote History Provider `pgHubSpoke`. However, data is not flowing and I see the following symptoms:

1. **Logs in Edge:** I see `I/O exception (org.apache.http.NoHttpResponseException)` when trying to reach the Standard Gateway on port 8060.

2. **Store & Forward:** On the Edge side, I see many data points going into **Quarantine**.

3. **Logs mention:** `Historian syncable 'edHistorian' is starting. Will synchronize data to remote historian 'pgHubSpoke' on server 'igResidual'`.

**What I've checked so far:**

- The System Name of the Standard Gateway matches the "Remote Gateway Name" in Edge Sync Settings.

- The provider name `pgHubSpoke` exists and is running on the Standard Gateway.

- The Tag History module is running on both Gateways.

**Questions:**

1. Are there specific **Service Security** settings in the Standard Gateway (under Gateway Network Services -\> History Sync) that I should verify beyond setting the Access Level to "Allow All"?

2. Does the fact that the remote provider is a **Historian Splitter** instead of a direct SQL Historian affect the Edge Sync capability?

3. Why would I be getting `NoHttpResponseException` if the Gateway Network status shows as "Connected"?

Any advice on how to debug the quarantine or the connection would be greatly appreciated. Thanks!

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 14, 2026, 2:05pm UTC](https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532/2 "2026-05-14T14:05:52Z")

</div>

> [@bsantaella](#):
>
> I see `I/O exception (org.apache.http.NoHttpResponseException)` when trying to reach the Standard Gateway on port 8060

That suggests that the gateway network is not set up correctly.

Also, is the central gateway also v8.3? If not, it won't work at all.

---

<div class="post-metadata">

**Author:** ![bsantaella](https://avatars.discourse-cdn.com/v4/letter/b/7cd45c/32.png) [@bsantaella](https://forum.inductiveautomation.com/u/bsantaella)\
**Post date:** [May 14, 2026, 2:20pm UTC](https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532/3 "2026-05-14T14:20:39Z")

</div>

Yes, both Gateways are running in version 8.3

---

<div class="post-metadata">

**Author:** ![ansari.fouad1990](https://avatars.discourse-cdn.com/v4/letter/a/85f322/32.png) [@ansari.fouad1990](https://forum.inductiveautomation.com/u/ansari.fouad1990)\
**Post date:** [May 22, 2026, 1:09am UTC](https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532/4 "2026-05-22T01:09:38Z")

</div>

@bsantaella Did you find a resolution? asking because I am having similar issues.

---

<div class="post-metadata">

**Author:** ![Chris\_Bingham](https://avatars.discourse-cdn.com/v4/letter/c/e5b9ba/32.png) [@Chris\_Bingham](https://forum.inductiveautomation.com/u/Chris_Bingham)\
**Post date:** [May 22, 2026, 4:07pm UTC](https://forum.inductiveautomation.com/t/issues-syncing-tag-history-from-ignition-edge-to-standard-gateway-history-sync/115532/5 "2026-05-22T16:07:08Z")

</div>

While the root cause to your issue might not be related, everyone should upgrade beyond 8.3.1 before troubleshooting Edge historian sync issues.  
Related post:

> [@Ignition Edge 8.3 Sync not working](https://forum.inductiveautomation.com/t/ignition-edge-8-3-sync-not-working/112218/6):
>
> Just wanted to chime in and confirm that this issue was addressed in 8.3.3: Improved Edge Historian sync performance by optimizing tag definition queries that were causing expensive temporary B-Tree operations on large datasets. If you encounter any other Remote Sync issues on 8.3.3+, please let us know. Thanks!