Potentially, or it may be that it takes 20 seconds for the device to figure out a lack of connection. This is what showed in the logs;  
and the issue was resolved by allowing None. This was using 8.1, I see in

[this thread](https://forum.inductiveautomation.com/t/opc-ua-client-connection-issues/79799/18) that things were refactored in 8.3 to be less strict.