# Localhost - connect Kepserver to Ignition

**URL:** <https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871>\
**Category:** Ignition\
**Tags:** opcua, ignition81\
**Created:** [May 24, 2024, 1:37pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871 "2024-05-24T13:37:41Z")\
**Posts on this page:** 13\
**Page:** 1

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [May 24, 2024, 1:37pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/1 "2024-05-24T13:37:41Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/7/279a1f3c46b60f1a6ca4bed2f606a77a773a5765.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/d/5dc01cf7503f36fd5a4947faa639d98dfbd0a132.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/4/5430cdbaf835ffcdecd98e9ac9935f7ad63fbe44.png)

But it is not connecting:

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/6/762cc45db9bd20705db0057e350c095e2b3f5deb.png)

Maybe I forgot something to config on KepServerEX6

---

<div class="post-metadata">

**Author:** ![Transistor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/transistor/32/3380_2.png) [@Transistor](https://forum.inductiveautomation.com/u/Transistor)\
**Post date:** [May 24, 2024, 1:44pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/2 "2024-05-24T13:44:33Z")

</div>

I removed the Perspective tag. This problem is not related to Perspective.

---

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [May 24, 2024, 2:05pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/3 "2024-05-24T14:05:46Z")

</div>

> [@Transistor](#):
>
> related to Perspective

thank you, it was an error

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [May 24, 2024, 2:18pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/4 "2024-05-24T14:18:28Z")

</div>

Make sure you've exported the certificate out of Kepware and Ignition and imported them into each other as approved/accepted certificates. Also, you MUST create a user inside Kepware with a password and make sure it has appropriate permissions. It's been a while since I set up a system with Kepware, but I remember the hangup I had was creating a user in Kepware and once I did that I got it working.

---

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [May 24, 2024, 2:39pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/5 "2024-05-24T14:39:05Z")

</div>

> [@michael.flagler](#):
>
> exported the certificate out of Kepware

I can export certificate of Kepware but I can't find where I can export and import certificate of Ignition on gateway

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [May 24, 2024, 2:40pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/6 "2024-05-24T14:40:13Z")

</div>

Under OPC-UA --\> Security

---

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [May 24, 2024, 3:14pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/7 "2024-05-24T15:14:19Z")

</div>

Thank you.  
but I only change `OPC UA` option to `OPC-DA COM Connection `and it work.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/d/dd0e5130b575d076c00c70f83b702d798e22408c.png)  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/5/557a1734293366540180a65f85b700d390d18d8f.png)

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [May 24, 2024, 3:15pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/8 "2024-05-24T15:15:37Z")

</div>

Personally, I wouldn't use OPC-DA. Less security, outdated, and most everything is moving away from OPC-DA. Probably less efficient also, but I don't know details about it. I avoid it whenever possible.

---

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [May 24, 2024, 3:40pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/9 "2024-05-24T15:40:58Z")

</div>

Thank you, I do what you recommended me. OPC UA work, but I can't find name of device that I have configured.

---

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [May 24, 2024, 3:45pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/10 "2024-05-24T15:45:32Z")

</div>

When I used OPC-DA, I find all devices

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/e/5eea622a65703230e2d6271175a8708fbfbbfcbe.png)

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [May 24, 2024, 4:15pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/11 "2024-05-24T16:15:25Z")

</div>

I don't recall if there are any permissions to allow it or not. What I do recall is that when using at least AB PLCs, I wasn't able to browse the tags because Kepware required that I uploaded the tag database from the PLC in order to do so, and we don't like doing that, so we couldn't browse down to tags like we could when using the Ignition OPC-UA server.

You probably don't need to set the group to Administrators like I did, but check what group the user you created is a member of and move them to either Administrators or Anonymous Clients.

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/e/5e1bf7a8ad8dc3e43a27e79a34f8001d81fb64b3.png)

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/0/2/022a74c4635d76fd75d07f1a7a7751c91f06ef76.png)

---

<div class="post-metadata">

**Author:** ![Francisco.Mejia](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/francisco.mejia/32/63246_2.png) [@Francisco.Mejia](https://forum.inductiveautomation.com/u/Francisco.Mejia)\
**Post date:** [May 30, 2024, 1:29pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/12 "2024-05-30T13:29:47Z")

</div>

Unfortunately, there are many plants still using DA. If the OPC server is installed in the same box as the gateway it is exposed to the same risk as the gateway protected by firewalls configuration to the upper layer of Purdue reference model network segmentation.

---

<div class="post-metadata">

**Author:** ![sebastien\_ng](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/sebastien_ng/32/55297_2.png) [@sebastien\_ng](https://forum.inductiveautomation.com/u/sebastien_ng)\
**Post date:** [June 7, 2024, 12:13pm UTC](https://forum.inductiveautomation.com/t/localhost-connect-kepserver-to-ignition/90871/13 "2024-06-07T12:13:26Z")

</div>

> [@michael.flagler](#):
>
> groupe l'utilisateur que vous avez créé est membre et déplacez-le vers Administrateurs ou Clients anonymes.

Thank you, I do what you recommended me