I’m on Ignition version: **8.1.17 (b2022051210)**. I’m connected to a CompactLogix version 31.013. I’m experiencing the following issue: an array of 150 **REAL** PLC tags shows incorrect data for each item that is smaller then 1E-4. When an item is smaller than 1E-4, the corresponding tag shows up as 0 in the tag browser (no matter how many decimal places I configure). Even if the PLC guy changes the value in LogixStudio, no reaction is shown in Ignition tag browser, unless he sets something greater than the magic 1E-4.  
Any known issue in the Logix driver?

Thanks, regards

---

<div class="post-metadata">

**Author:** ![lrose](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/lrose/32/62724_2.png) [@lrose](https://forum.inductiveautomation.com/u/lrose)\
**Post date:** [July 11, 2022, 2:48pm UTC](https://forum.inductiveautomation.com/t/logix-driver-and-real-data-issue/61739/2 "2022-07-11T14:48:14Z")

</div>

If you edit the tag, does the value show up there?

The reason I ask is because I recently found that very small numbers didn’t show in the Tag Browser, but if I edited the tag, then the value was shown.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 11, 2022, 2:52pm UTC](https://forum.inductiveautomation.com/t/logix-driver-and-real-data-issue/61739/3 "2022-07-11T14:52:36Z")

</div>

Sounds like you still have the default deadband of 1E-4 configured on your tags.

---

<div class="post-metadata">

**Author:** ![pgmo](https://avatars.discourse-cdn.com/v4/letter/p/d07c76/32.png) [@pgmo](https://forum.inductiveautomation.com/u/pgmo)\
**Post date:** [July 11, 2022, 3:08pm UTC](https://forum.inductiveautomation.com/t/logix-driver-and-real-data-issue/61739/4 "2022-07-11T15:08:21Z")

</div>

> [@Kevin.Herron](#):
>
> Sounds like you still have the default deadband of 1E-4 configured on your tags

Many thanks, Kevin, you are right: I set the deadband to 1E-7 and it works perfect!  
Thanks, regards