# Logix Driver fails to read/write CompactLogix 5380 Tags

**URL:** <https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709>\
**Category:** Ignition\
**Created:** [November 4, 2021, 9:47am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709 "2021-11-04T09:47:46Z")\
**Posts on this page:** 10\
**Page:** 1

<div class="post-metadata">

**Author:** ![Falconb](https://avatars.discourse-cdn.com/v4/letter/f/22d042/32.png) [@Falconb](https://forum.inductiveautomation.com/u/Falconb)\
**Post date:** [November 4, 2021, 9:47am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/1 "2021-11-04T09:47:46Z")

</div>

Ignition 7.9.17  
Logix Driver 3.9.17

Hi, We are using the latest Rockwell CompactLogix 5380 PLC running firmware 28 and using Ignition 7.9.17 to develop our project. I have found the Ignition project can’t read any of the PLC tags, showing bad quality errors.  
Without any changes to the Ignition project, if I connect to the older CompactLogix 5370 running firmware 28 with exactly the same PLC code, tag structure and network settings etc, the Tag read/writes work.

- The quick client OPC browser fails to find any of the 5380 tags but finds the 5370 tags.
- I have check the access permissions of these tags in the PLC and they are either external read only or read/write access.
- There is no security enabled in the either PLC.
- I can’t find any other permission settings in the PLC’s.

Has anyone else experienced this issue with the CompactLogix 5380 and Ignition7.9?  
Or confirm that they have a working Ignition project (v7 or 8) with a CompactLogix 5380 running v28?

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [November 4, 2021, 10:41am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/2 "2021-11-04T10:41:47Z")

</div>

Not sure if it’s helpful, but before upgrading to v8, I was at 7.9.9 using a set of 5069-L310ER PLCs at firmware v30 with no issues.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 4, 2021, 10:49am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/3 "2021-11-04T10:49:59Z")

</div>

> [@Falconb](#):
>
> The quick client OPC browser fails to find any of the 5380 tags

This is probably the important part. Can you upload your logs?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 4, 2021, 11:03am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/4 "2021-11-04T11:03:26Z")

</div>

In the screenshots you sent support there are a couple of the web status page from the 5380 - can you get another that includes both the IP in the address bar and shows the “Browse Chassis” page?

---

<div class="post-metadata">

**Author:** ![Falconb](https://avatars.discourse-cdn.com/v4/letter/f/22d042/32.png) [@Falconb](https://forum.inductiveautomation.com/u/Falconb)\
**Post date:** [November 5, 2021, 4:41am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/5 "2021-11-05T04:41:07Z")

</div>

Hi Kevin, thanks for responding.  
Note there are no IO modules connected to the 5380 chassis, we are using a ControlLogix remote IO rack and a Wago 750 remote IO rack over EtherNet/IP.  
Attached is the requested screenshot.

 ![CompactLogix5380-08](https://us1.discourse-cdn.com/inductiveautomation/original/3X/1/3/1360b67206225fc1ceb18f1f3fdaf9853e60fac6.png)

---

<div class="post-metadata">

**Author:** ![Arnaud\_Declerck](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/arnaud_declerck/32/44872_2.png) [@Arnaud\_Declerck](https://forum.inductiveautomation.com/u/Arnaud_Declerck)\
**Post date:** [November 5, 2021, 5:07am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/6 "2021-11-05T05:07:48Z")

</div>

Hi @Falconb,

I have a 5380 plc here, I will test it and let you know if I find something. Just also beware that v28 is not a great version of firmware. I've got in the past a lost of issues with it (complete lost of plc program).

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [November 5, 2021, 11:25am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/7 "2021-11-05T11:25:50Z")

</div>

Have you made sure that the PLC is set up for Dual IP mode and not DLR?

---

<div class="post-metadata">

**Author:** ![Falconb](https://avatars.discourse-cdn.com/v4/letter/f/22d042/32.png) [@Falconb](https://forum.inductiveautomation.com/u/Falconb)\
**Post date:** [November 7, 2021, 8:34am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/8 "2021-11-07T08:34:27Z")

</div>

As far as I can see there are no options to set DLR in v28, v30 has this option under controller properties

 ![CompactLogix5380-09](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/c/3c744e4c37af70d5647f24de6dd2a27c8c928e9b.png)

However as per Jordan’s comment above, that he has had v30 running with Ignition 7.9, so I upgraded my Studio 5000 and the 5380 to v30 and now the Ignition Project Tag read/writes and OPC Quick Client are now working.

So there appears to be a problem or a setting that I couldn’t find, with 5380 v28 and Ignition 7.9.17 Logix driver.

---

<div class="post-metadata">

**Author:** ![Falconb](https://avatars.discourse-cdn.com/v4/letter/f/22d042/32.png) [@Falconb](https://forum.inductiveautomation.com/u/Falconb)\
**Post date:** [November 7, 2021, 8:35am UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/9 "2021-11-07T08:35:46Z")

</div>

Thanks Jordan, I updated the 5380 to v30 and now Ignition is working,

---

<div class="post-metadata">

**Author:** ![Arnaud\_Declerck](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/arnaud_declerck/32/44872_2.png) [@Arnaud\_Declerck](https://forum.inductiveautomation.com/u/Arnaud_Declerck)\
**Post date:** [November 8, 2021, 3:46pm UTC](https://forum.inductiveautomation.com/t/logix-driver-fails-to-read-write-compactlogix-5380-tags/52709/10 "2021-11-08T15:46:35Z")

</div>

hi @Falconb,

Sorry, i didn't have time to test it. But glad you have found your issue.