I've got a project using Sepasoft's Track module and they're helping me resolve an issue.

The problem is, when I give them my log file from the MES Support Package download, it's full of LogixDriver warnings that absolutely flood the file (50197 rows out of 50222), making it hard to read.

The warnings look like this:  
Unhandled CIP type: LTIMEdrivers.LogixDriver.Requests.ReadStructuredTagsRequestWARNu0opc-ua-executor-116514

Should I be worried about these warnings? How can I resolve them? If it's typical, can I disable them?

Thanks,  
-Colin

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [February 10, 2023, 1:06pm UTC](https://forum.inductiveautomation.com/t/logixdriver-warnings-flooding-log-file/69688/2 "2023-02-10T13:06:25Z")

</div>

Rockwell introduced new primitive datatypes in recent firmware versions, including LTIME. If you really need these, you might consider testing my new EtherNet/IP driver, which should support these. It is in beta, and not tested much on these types, but I wouldn't mind a data point:

> [@Automation Professionals' EtherNet/IP Communication Suite V2](https://forum.inductiveautomation.com/t/automation-professionals-ethernet-ip-communication-suite-v2/68190/31):
>
> New beta. Couple items: Suppressed a super-noisy warning that would flood the logs while connecting and probing and during even the slightest comms hiccup. Significantly reduced memory pressure throughout the module by implementing SoftReference caching for byte[] and ByteBuffer instances, using stepped sizes (8, 12, 16, 24, 32, 48, 64, 96...). The GC can still reclaim them when it needs to, but it makes it possible to skip new object creation when used and released instances are hanging…

However, I suspect you aren't actually using these tags (or you'd have found this problem earlier). Which suggests that someone dragged and dropped an entire tag hierarchy from the OPC browser to Ignition's tag browser, creating subscriptions to everything. That is an extremely bad practice.