# M580 OPC-UA Module

**URL:** <https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179>\
**Category:** Ignition\
**Created:** [April 29, 2021, 7:57pm UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179 "2021-04-29T19:57:56Z")\
**Posts on this page:** 6\
**Page:** 1

<div class="post-metadata">

**Author:** ![jay](https://avatars.discourse-cdn.com/v4/letter/j/ed8c4c/32.png) [@jay](https://forum.inductiveautomation.com/u/jay)\
**Post date:** [April 29, 2021, 7:57pm UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179/1 "2021-04-29T19:57:56Z")

</div>

Has anyone used the OPC-AU module that is available for the Modicon M580 PLC. Does it work with Ignition? Any snags?

[BMENUA0100](https://www.se.com/ww/en/product/BMENUA0100/opc-ua-module-for-m580/)

---

<div class="post-metadata">

**Author:** ![tgfgreaves](https://avatars.discourse-cdn.com/v4/letter/t/919ad9/32.png) [@tgfgreaves](https://forum.inductiveautomation.com/u/tgfgreaves)\
**Post date:** [June 23, 2021, 12:57am UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179/2 "2021-06-23T00:57:06Z")

</div>

Interested in this also.

---

<div class="post-metadata">

**Author:** ![seano](https://avatars.discourse-cdn.com/v4/letter/s/d2c977/32.png) [@seano](https://forum.inductiveautomation.com/u/seano)\
**Post date:** [July 6, 2023, 10:38pm UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179/3 "2023-07-06T22:38:21Z")

</div>

Did this work in the end?

---

<div class="post-metadata">

**Author:** ![Chris\_Taylor](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/chris_taylor/32/3315_2.png) [@Chris\_Taylor](https://forum.inductiveautomation.com/u/Chris_Taylor)\
**Post date:** [July 9, 2023, 12:40pm UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179/4 "2023-07-09T12:40:07Z")

</div>

We had a customer that had these, horrible to setup and not entirely reliable. Reverted back to Modbus after 4 months.

---

<div class="post-metadata">

**Author:** ![j.israelsen](https://avatars.discourse-cdn.com/v4/letter/j/ad7895/32.png) [@j.israelsen](https://forum.inductiveautomation.com/u/j.israelsen)\
**Post date:** [July 10, 2023, 3:41pm UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179/5 "2023-07-10T15:41:00Z")

</div>

The original firmware for the NUA was troublesome to say the least. There have been recent firmware updates that resolved some major issues, I would recommend utilizing the latest firmware (v2.02 when this is posted). I have generally used the "Standard" mode, I haven't had much experience with the "Secured" mode. I've had pretty good success with the "Standard" mode.

I've used it with some other HMI platforms (not Ignition). I lightly dabbled with the module utilizing Ignition. There was at one time a bug where Ignition didn't interface with the module well (it kept dropping connections or not connecting at all) but I believe that was resolved a year or two back with an Ignition patch/update.

It's pretty hard to say no to the module when you get all of the benefits of OPC-UA (versus Modbus). However, of course, Modbus works.

---

<div class="post-metadata">

**Author:** ![Scott\_Alexander](https://avatars.discourse-cdn.com/v4/letter/s/8edcca/32.png) [@Scott\_Alexander](https://forum.inductiveautomation.com/u/Scott_Alexander)\
**Post date:** [March 14, 2024, 12:14am UTC](https://forum.inductiveautomation.com/t/m580-opc-ua-module/46179/6 "2024-03-14T00:14:51Z")

</div>

So, not an Ignition experience per se, but we installed these on a project (late 2023) with iFix as the front end and basically a Kepware OPC-UA client. Seemed reliable enough and honestly the stuff we ran into I'd blame on the iFix side. Having said that, we are going for redundant racks and these cards will not "swap" IP addresses on rack failure like most of the M580 comm cards. S.E. promised new firmware would take care of this, but no firmware as of March 2024