# Mapping network drive confusion

**URL:** <https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338>\
**Category:** Ignition\
**Created:** [April 4, 2024, 11:28am UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338 "2024-04-04T11:28:07Z")\
**Posts on this page:** 18\
**Page:** 2

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 19, 2024, 1:50pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/21 "2024-04-19T13:50:16Z")

</div>

I need the external script because I can not access the network drive. The ignition service could not run under the different account, as it's on a different domain than what our server is on.

It's the only work around I could come up with.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 19, 2024, 1:59pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/22 "2024-04-19T13:59:33Z")

</div>

> [@Miguel\_Villasenor\_Es](#):
>
> work around

Are you sure this will work? (I would expect it to not work, as the python will run with the same credentials as the Ignition service.)

I think you need to change your architecture, or get IT to put in the appropriate cross-domain trust relationships.

---

<div class="post-metadata">

**Author:** ![JordanCClark](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/jordancclark/32/83362_2.png) [@JordanCClark](https://forum.inductiveautomation.com/u/JordanCClark)\
**Post date:** [April 19, 2024, 2:07pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/23 "2024-04-19T14:07:13Z")

</div>

> [@Miguel\_Villasenor\_Es](#):
>
> It's the only work around I could come up with.

But it's not working. As evidenced by the _Did not work ;(_ message.

EDIT: Sorry, got interrupted for a bit. The reason it didn't work is that system.util.execute will run under the same user that runs it. The service still doesn't have access to the share.

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 19, 2024, 3:41pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/24 "2024-04-19T15:41:32Z")

</div>

Wait what do you mean the same "user that runs it"? Are you talking about the ignition client user or the local system user? As in, my user account for ignition is villm24, that's who it's running under?

 ![Capture](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/1/3117053c5e95d48fb84d1f8b332e5d615a725502.png)

Given the image, the account that's currently logged in is the administrator account correct?

The ignition service is running under local system, which would be the administrator account correct?

The external script is using an account that has access to the drive. When I run the script via the python console, it works great. No issues what so ever. If I run it using system.util.execute, nothing happens, I don't get any errors anywhere.

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 19, 2024, 3:43pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/25 "2024-04-19T15:43:37Z")

</div>

I'm not sure if it'll work, I'll have to keep trying. You guys know more than me. If corporate would give our account access to their domain/resources this thread wouldn't exist.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 19, 2024, 3:53pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/26 "2024-04-19T15:53:48Z")

</div>

> [@Miguel\_Villasenor\_Es](#):
>
> The ignition service is running under local system, which would be the administrator account correct?

No, the Local System account has no network privileges. You need to run the service itself (that service config page) as a suitable domain user. Nothing to do with logging into Ignition. This is Ignition (the service) gaining credentials on your network.

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 23, 2024, 2:25pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/27 "2024-04-23T14:25:29Z")

</div>

I've tried many many solutions up until now. Corporate is making things difficult, but I hope they go through and allow the IT team to give us access to the drive.

One last question, as I've exhausted all possibilities I believe, **can the ignition service run under an account from a different domain?** If not I'll request that our administrator account have trust access.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 23, 2024, 2:34pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/28 "2024-04-23T14:34:48Z")

</div>

I wouldn't think so, unless the domains trust each other.

Trust is domain to domain, not account to domain, IIUC.

{ I'm not a Windows expert, fwiw. I avoid it ~~like the plague~~ _because it is a plague_. }

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [April 23, 2024, 3:20pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/29 "2024-04-23T15:20:26Z")

</div>

While I haven't had the need to map drives using Ignition, in reading through this thread, I think your best bet is to go back to how you were originally doing it due to the fact that you're needing to use alternate credentials on a different domain. I think where you were messing up according to @JordanCClark is that you were mapping the drive M to `\\<REDACTED>\cad\cad2\drawings2\` but then using `M:\\<REDACTED>\cad\cad2\2` and getting an error that it's not a directory. You have to keep in mind that it's appending that path onto your original drive mapping, so the path you were essentially trying to access was `\\<REDACTED>\cad\cad2\drawings2\<REDACTED>\cad\cad2\2` which probably doesn't exist, which is why you got the error.

So in another example you gave, you would probably go back to your original network mapping, then your input path or param1 would be `M:\0\Current\0W390082-.GP4` substituting the proper slashes as I'm not sure how Ignition will want them. The other issue you're going to have is this will execute on the gateway since you're using perspective (maybe that's your intent), so it won't be on the user's PC, but on the gateway where it downloads the file.

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 24, 2024, 11:56am UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/30 "2024-04-24T11:56:28Z")

</div>

Right, the idea is to copy one of those drawings to a local folder where it is accessible to ignitions gateway, at which point we can use some of ignitions functions to download the file to the clients computer.

**Ok, I'll give it another shot! So use the wrapper right and restart the service, then when I go to invoke the drive in script just use M:\0\current\somefile.gp4?** I swear I've already done this, but I'll try again and let you guys know how it goes. _Lastly, is what I have correct?_  
 ![wrapper](https://us1.discourse-cdn.com/inductiveautomation/original/3X/6/e/6e01d5848f57f0b38e66ed8c3b2e320eb91de778.png)

> [@michael.flagler](#):
>
> then your input path or param1 would be `M:\0\Current\0W390082-.GP4` substituting the proper slashes as

I will try this as well, although when I was doing that on my laptop I would get an error from the **subprocess** module that said something to the affect of _"There's already one connection to the server, you can not have any more than one",_ which lead me to unmapping the drive on my computer for it to work.

**Sorry I've been hard to work with, to everyone on this post, I appreciate the help and will do my best to browse the forums and help others where I can. I'm glad this community is helpful and kind.**

---

<div class="post-metadata">

**Author:** ![michael.flagler](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/michael.flagler/32/26272_2.png) [@michael.flagler](https://forum.inductiveautomation.com/u/michael.flagler)\
**Post date:** [April 24, 2024, 9:39pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/31 "2024-04-24T21:39:45Z")

</div>

I've played with this and here's my the relevant lines from my working ignition.conf file:

```python
wrapper.share.1.location=\\<REDACTED>\Projects
wrapper.share.1.target=P:
wrapper.share.1.type=DISK
wrapper.ntservice.account=Ignition
wrapper.ntservice.password=<REDACTED>
wrapper.share.1.account=<REDACTED>
wrapper.share.1.password=<REDACTED>
wrapper.share.1.shutdown.unmap=TRUE
wrapper.share.1.startup.max_retries=2
wrapper.share.1.startup.retry_interval=10

```

For the ntservice account/password I used the local account of the username/password the Ignition service was running under (in my case it was a local account). For the share account, I connected to a domain (computer was not connected to this domain and even on a different network, so it was routed), but was in the form of `DOMAIN\username`

One note is that your share location cannot end in a backslash - even the Tanuki documentation mentions that this will break it. See: [wrapper.share.\<n\>.\* Properties - Java Service Wrapper](https://wrapper.tanukisoftware.com/doc/english/prop-share-general.html)

I also enabled the `wrapper.debug=TRUE` for testing and found in the logs the following (wasn't necessary to use debug for this, but when it wasn't working, this gave me the error - just make sure to comment it back out when done testing):

```python
INFO | wrapper | 2024/04/24 14:25:51 | Attempting to map the "\\<REDACTED>\Projects" share to "P:"...
INFO | wrapper | 2024/04/24 14:25:51 | Mapped "P:".

```

Once working, I just accessed the file such as `system.file.fileExists('P:\myfile.txt')`

Another note...this does NOT work in Linux. This seems to be Windows onlym and you must be using a separate account for the Ignition service (it won't work running as LOCAL SYSTEM).

> **[Mapping a Network Drive | Ignition User Manual](https://docs.inductiveautomation.com/docs/8.1/tutorials/tutorials-and-helpful-tricks/mapping-a-network-drive)**
>
> Learn how to make a network drive available to Ignition

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 24, 2024, 10:55pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/32 "2024-04-24T22:55:58Z")

</div>

Also be aware that if your target share is not available when Ignition is restarted, Ignition will take longer to start up, due to those retries. And if your target share ever disconnects, it won't reconnect until you restart the Ignition service.

Using the service wrapper's drive mapping ability is **not** fit for production use. Full stop.

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 25, 2024, 2:34pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/33 "2024-04-25T14:34:14Z")

</div>

I haven't tried it out yet as we need to restart the ignition service, But this has to be the solution. I was using the same domain/user for the .ntservice when I probably should have been using our local account....  
🤦🏾‍♂️

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 25, 2024, 4:04pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/34 "2024-04-25T16:04:56Z")

</div>

I was thinking about what you wrote.

> [@pturmel](#):
>
> And if your target share ever disconnects, it won't reconnect until you restart the Ignition service.

If we lose connection to the mapping, we won't be able to access the drive which is fine, but it won't affect other systems tied to ignition will it? I don't mind it disconnecting and having to wait till end of production to restart the service and remap the drives, I just don't want ignition to come to a halt because a mapped drive was disconnected.

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [April 25, 2024, 4:28pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/35 "2024-04-25T16:28:13Z")

</div>

> [@Miguel\_Villasenor\_Es](#):
>
> systems tied to ignition will it?

No, just whatever you configured in Ignition to use that mapped drive will be affected.

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [April 26, 2024, 12:33pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/36 "2024-04-26T12:33:59Z")

</div>

Worked like a charm!!!!  
🥹 🥹 🥹

---

<div class="post-metadata">

**Author:** ![Miguel\_Villasenor\_Es](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/miguel_villasenor_es/32/60416_2.png) [@Miguel\_Villasenor\_Es](https://forum.inductiveautomation.com/u/Miguel_Villasenor_Es)\
**Post date:** [May 2, 2024, 12:20pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/37 "2024-05-02T12:20:56Z")

</div>

One last question please.

I will be meeting with a "security" team member and he's going to ask me how the Ignition platform is going to access the network drive. **I am 100 percent certain his main question is going to "is it using clear text to establish a connection and what protocol and ports will this be happening on?** I am not to versed in Ignition to answer that, could you please provided us with some information regarding this please?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [May 2, 2024, 12:33pm UTC](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338/38 "2024-05-02T12:33:13Z")

</div>

Ignition itself doesn't make the connection. It delegates to the Windows OS with either the credentials supplied in `ignition.conf` for a drive letter mapping, or the implicit credentials of the service user for UNC paths (not using a drive letter).

Have your IT team **read this entire topic**.

Ask them to help you use UNC paths for the most robust implementation.

[Previous page](https://forum.inductiveautomation.com/t/mapping-network-drive-confusion/88338.md?page=1)