How do scanclasses affect memory tags?

We are trying to optimize the performance of our tag providers and I was curious if changing the scan rate on memory tags will accomplish anything. Does Ignition actually ‘scan’ anything in regards to memory tags?

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [October 8, 2020, 3:15pm UTC](https://forum.inductiveautomation.com/t/memory-tag-scanclass/39502/2 "2020-10-08T15:15:42Z")

</div>

> [@levi\_jacobs](#):
>
> Does Ignition actually ‘scan’ anything in regards to memory tags?

No, the scan class rate (or tag group rate in 8.x) is irrelevant for memory tags.

---

<div class="post-metadata">

**Author:** ![levi\_jacobs](https://avatars.discourse-cdn.com/v4/letter/l/ba9def/32.png) [@levi\_jacobs](https://forum.inductiveautomation.com/u/levi_jacobs)\
**Post date:** [October 8, 2020, 3:16pm UTC](https://forum.inductiveautomation.com/t/memory-tag-scanclass/39502/3 "2020-10-08T15:16:21Z")

</div>

Thanks for the quick reply!