<div class="post-metadata">

**Author:** ![ggross](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ggross/32/12668_2.png) [@ggross](https://forum.inductiveautomation.com/u/ggross)\
**Post date:** [May 15, 2023, 6:03pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/1 "2023-05-15T18:03:27Z")

</div>

We are excited to announce the availability of our Mitsubishi driver that will be included in the 8.1.28 release and is currently available in the 8.1 nightly release.

## Mitsubishi TCP Driver

The Mitsubishi TCP driver provides a user interface in the Gateway to designate mapped addresses when connected to devices that support the MELSEC protocol. After setup, configured tags will be browsable in the OPC Browser of the Designer with read and write (where applicable) access. Supported Hardware Series include:

- iQ-R
- iQ-F
- Q
- L

## Connect to Mitsubishi devices

Before you can connect your Mitsubishi device to this driver, make sure your programmed device settings meet the driver requirements. Detailed setting requirements are included in the GX Works Configuration section.

1. Navigate to Config \> OPC UA \> Device Connections on the Gateway Webpage.
2. On the Devices page, click on Create new Device.
3. Select Mitsubishi TCP, and click Next.
4. Fill in the Name field. Entering a description is optional.
5. Select the MELSEC series you will be connecting to using the dropdown. Options include iQR, iQF, Q, and L.
6. Enter the device hostname in the Hostname field.
7. Enter the device port in the Port field.  
 ![](https://us1.discourse-cdn.com/inductiveautomation/original/3X/4/c/4c7f262fb77c1a5b62c52697d5e319bb0c4f08d4.png)
8. Enter the local address of the network adapter to connect from. This is necessary if you have multiple network cards and you need to specify the particular network card that has PLC access.
9. Leave the default values in the remaining fields.
10. Click Create New Device.

The Devices page now displays the Mitsubishi TCP device is successfully connected. If an `Idle` state is noted, your Mitsubishi device is likely not configured in a manner that allows multiple connections on the port you have selected.

## Device Settings

| General | Description |
| --- | --- |
| Name | Device name |
| Description | Device description |
| Enabled | If true, attempt connection to the device, default is true |
| Main | Description |
| Series | The series of the Mitsubishi device. Default is iQR |
| Hostname | The IP Address of the device |
| Port | The port the device is listening on |
| Local Address | Address of network adapter to connect from |
| Timeout | The request timeout, specified in milliseconds with a valid range from 0 to 16383750. Default is 5000 |
| Request Optimization | Description |
| Max Gap Size | The maximum address “gap” to span when optimizing requests to contiguous address locations. Increasing the max gap size will reduce the number requests but increase the amount of data requested. Default is 0. |
| Write Priority Ratio | The number of write requests to execute for every read request when an abundance of both types are queued up for execution. Default is 5. |

## Addressing

You can add addresses by entering the Browse Path and Address information individually (via the device address page, or directly in the Tag Editor in the Designer using a valid opcItemPath) or importing a CSV file containing a list of addresses to upload at once. The addresses page is setup to read three areas of address information to generate an Ignition OPC address:

- Browse Path: This will be the location represented in Ignition's OPC UA Browser. The last item should be the node itself, but nested folder structures separated by `/` are supported. e.g. A browse path of `M/M0` will result in the following:  
 ![QLU](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/b/7ba5654eb803149222c90caea9a4e9e8d3dd4aad.png)
- Address: This is the device, offset, and additional specifications to find desired values.
- Description: This is an optional field to help in identifying displayed values.

To access the addresses page on the Gateway:

1. Go to the Config \> OPC UA \> Device Connections.
2. Click the More dropdown and choose addresses on your Mitsubishi device.  
 ![](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/d/2d46822b95479c9fd0e66acfe764791a8dd6e770.png)

### Adding Individual Address Rows

Even if you are planning to import multiple addresses using a CSV file, it’s recommended to first enter a single tag address to test if your connection is working as expected.

 ![MitsubishiAddresses](https://us1.discourse-cdn.com/inductiveautomation/original/3X/5/e/5e44f73b4f452ddba3d54741bc5ea064d2905cfe.png)

To enter addresses:

1. Click Add Row to populate rows for address information.
2. Enter Browse Path field and Address field information. Enter Description information as desired.  
Note: All components are case-insensitive.
3. Continue adding rows and address information until you’ve added all the addresses you want to be available as tags.
4. Click Save Configuration when you are finished.

### Importing and Exporting

To Import a CSV file:

1. Select Load Configuration File on the device address page.
2. Select Choose File.
3. Locate the CSV file you want to upload and select it to open.  
Note: A comma separates column information. If your Description column includes commas, use quotes to prevent misinterpretations when uploading.
4. Select the Append to current configuration box if you already have addresses listed and you want to add on to them. Leave unchecked if you want to replace existing rows.
5. Click Load.  
Note: If an existing address shares a browse path with an address imported by the CSV file, it will be replaced with the imported address.  
 ![LoadConfig](https://us1.discourse-cdn.com/inductiveautomation/original/3X/7/e/7e215d89932a5342f3a3c178e3d95ee4de764d7a.png)
6. Click Save Configuration.  
Click the Export Configuration ![](https://us1.discourse-cdn.com/inductiveautomation/original/3X/c/b/cbfbd485215dd868f16d5d269d7bcc9b910a45bc.png) icon to download the existing address rows as a CSV file.

### Determining Addresses

The Mitsubishi driver requires Area and Offset address components, but also allows many optional specifications. It’s important to know where the optional components must be placed in your address to properly connect. The example syntax below shows how optional data type (including modifiers) and array specifiers are listed before the Offset specification and the optional array element index and bit index must be listed after the Offset specification.

Note: This page uses the term Area to describe the address component that identifies the PLC device to eliminate confusion with other sections of this page, such as the Device Settings which applies to the Ignition Mitsubishi driver.

Example syntax, where optional components are included in curly brackets  
` Area{<DataType{[array]}>}Offset{.Bit} `

#### Areas (Devices)

The following table shows the device keyword recognized by the driver as well as the native type of each device. Extended Data Registers and Extended Link Registers are currently not supported.

| Area Name | Area | Area Native Type |
| --- | --- | --- |
| Special relay | SM | Bit |
| Special register | SD | Word |
| Input | X | Bit |
| Output | Y | Bit |
| Internal relay | M | Bit |
| Latch relay | L | Bit |
| Annunciator | F | Bit |
| Edge relay² | V | Bit |
| Link relay | B | Bit |
| Step relay | S | Bit |
| Data register | D | Word |
| Link register | W | Word |
| Timer Contact | TS | Bit |
| Timer Coil | TC | Bit |
| Timer Current value | TN | Word |
| Long timer¹ ² Contact | LTS | Bit |
| Long timer¹ ² Coil | LTC | Bit |
| Long timer¹ ² Current value | LTN | Double Word |
| Retentive timer Contact | STS | Bit |
| Retentive timer Coil | STC | Bit |
| Retentive timer Current value | STN | Word |
| Long retentive timer¹ ² Contact | LSTS | Bit |
| Long retentive timer¹ ² Coil | LSTC | Bit |
| Long retentive timer¹ ² Current value | LSTN | Double Word |
| Counter Counter Contact | CS | Bit |
| Counter Coil | CC | Bit |
| Counter Current value | CN | Word |
| Long counter¹ Contact | LCS | Bit |
| Long counter¹ Coil | LCC | Bit |
| Long counter¹ Current value | LCN | Double Word |
| Link special relay | SB | Bit |
| Link special register | SW | Word |
| Direct access input² | DX | Bit |
| Direct access output² | DY | Bit |
| Index register Index register | Z | Word |
| Long index register¹ | LZ | Double Word |
| File register Block switching method | R | Word |
| Serial number access method | ZR | Word |
| Refresh data register¹ ² | RD | Word |

¹ Not available for Q/L series  
² Not available for iQ-F series

#### Data Types

The Mitsubishi driver supports reading/writing data types larger than the area’s native type by combining bytes from adjacent offsets into a single value. For example, each Data Register (D) point is natively a word (16-bit), but reading D0 requests bytes for D0 and D1 and combines the bytes into a signed 32-bit value.

The Mitsubishi driver does not support reading/writing data types smaller than the area’s native type. For example, each Long Index Register (LZ) point is a double word (32-bit) which means LZ0 and LZ0 cannot be specified.

Some areas in particular cannot be combined and specific data types corresponding to its native type must be specified:

- Any area having a native type of Bit
- Any area having to do with Current value, such as:
- TN
- LTN
- STN
- LSTN
- CN
- LCN

**String Request Considerations**

When specifying a string data type, the length of the string must also be specified on the address. For example, `D<string10>0` requests a string of up to 10 characters at offset 0 in the data register device.

- If the length of the string is less than the address string length, it will be padded with null characters. For example, writing `hello` to `D<string10>` is equivalent to writing `hello\0\0\0\0\0` where `\0` are `null` characters.
- If the length of the string is more than the address string length, it will be truncated to the address string length. For example, writing `hello world!` to `D<string10>` is equivalent to writing `hello worl`.

For the Q/L series, the string length will be automatically rounded up to the nearest even value. This is because two characters are stored inside a word. For example, `D<string9>0` will be treated as `D<string10>0`.

#### Offsets

Depending on the PLC series and area, offsets can be specified in octal, decimal, or hexadecimal. In the case of octal offsets, if an unsupported offset is specified an `Error_Configuration` error will be returned.

| | iQ-R | iQ-F | Q | L |
| --- | --- | --- | --- | --- |
| **X** | Hex | Octal | Hex | Hex |
| **DX** | Hex | N/A | Hex | Hex |
| **Y** | Hex | Octal | Hex | Hex |
| **DY** | Hex | N/A | Hex | Hex |
| **B** | Hex | Hex | Hex | Hex |
| **SB** | Hex | Hex | Hex | Hex |
| **W** | Hex | Hex | Hex | Hex |
| **SW** | Hex | Hex | Hex | Hex |

Hexadecimal offsets are supported using traditional hexadecimal notation (0-F) for the offset. If specifying bit notation, the offset is traditional hexadecimal notation, but the bit designation is decimal (0-15).

Examples:

- `Y0F`: Area Y at offset F
- `SW0A.15`: Area SW at offset A, bit F

#### Optional Data Types

The following data types are recognized by the driver:

| Bool | Int16 | Int32 | Int64 | UInt16 |
| --- | --- | --- | --- | --- |
| **UInt16** | **UInt64** | **Float** | **Double** | **String** |

If the data type is omitted, a default data type will be used depending on the area’s native type:

| Area Native Type | Default Data Type |
| --- | --- |
| Bit | bool |
| Word | int16 |
| Double word | int32 |

**Optional Data Type Modifiers**

| Attribute | Order |
| --- | --- |
| @BE | Big Endian Byte Order |
| @LE | Little Endian Byte Order (default when not specified) |
| @HL | High-Low Word Order (default when not specified) |
| @LH | Low-High Word Order |

#### Optional Arrays

Arrays represent a contiguous range of addresses starting from an offset. For example, instead of reading `D<int16>0` through `D<int16>8`, you can create an array of the same values. The number of elements in an array are determined by multiplying the array dimensions. So reading `D<int16[3, 3]>0` is equivalent to reading 9 elements with the start offset is 0 and the last offset is 8.

Similarly, reading an element within an array is equivalent to reading a single address. For example, `D<int16[3, 3]>0[1][2]` is equivalent to reading `D<int16>5`.

| D[0][0] = D0 | D[0][1] = D1 | D[0][2] = D2 |
| --- | --- | --- |
| **D[1][0] = D3** | **D[1][1] = D4** | **D[1][2] = D5** |
| **D[2][0] = D6** | **D[2][1] = D7** | **D[2][2] = D8** |

Large arrays should be used with caution. If an array read/write request is too large to fit into a single request, it will be broken up into multiple non-atomic sequential requests. Splitting requests when writing can result in the first send of the write requests creating new values and the remaining write requests failing. Similarly, if read requests are sent separately the resulting array may contain stale points.

#### Optional Bit Index

A decimal bit index can be specified on any integer data type to retrieve a boolean value at some bit position. **Addresses with a bit index are read-only** and any attempts to write to them will result in a `Bad_NotSupported` error due to the MELSEC protocol not supporting atomic writes to bits within an underlying data type.

A simple example of reading a bit would be D0.0, which reads the bit0 of int16 at offset 0. You can also read bits within array elements that represent scalar values following the same addressing format. To read the bit 0 of element 0 of an array of length 4 at offset 0 would be `D<int16[4]>0[0].0`

A bit index cannot be specified for the following:

- Non-integer data types (bool, float, double, and string)
- Non-scalar addresses (arrays)

## GX Works Configuration

GX Works is the programming software designed for Mitsubishi PLCs. Before you can use the Mitsubishi driver, some configurations need to be made in GX Works when connecting to MELSEC-Q/L, iQ-F and iQ-R series devices with the Mitsubishi driver. These instructions are written for GX Works3. GX Works2 has slightly different settings but should in general resemble the following setting requirements.

1. Under the navigation tab, locate Parameter \> CPU \> Module Parameter \> Basic Settings \> Own Node Settings.
2. Set Enable/Disable Online Change to Enable All (SLMP).
3. Set Communication Data Code to Binary.
4. Navigate to External Device Configuration \> Detailed Setting to add an SLMP Connection Module to the Ethernet Configuration with Protocol set to TCP.
5. Make sure to also identify the IP Address and Port No. These settings are what will be used for the Mitsubishi TCP driver Hostname and Port connection fields.  
Note: If multiple connections to the PLC are required, multiple SLMP Connection Modules will need to be defined.
6. Write all changes to the PLC (Online \> Write to PLC) and initiate a power cycle.

### Configuring Device Points

Some areas or offsets within an area may not be accessible by default unless additional memory is allocated.

1. Navigate to Parameter \> CPU \> CPU Parameter \> Memory Device Setting \> Device/Label Memory Area Setting \> Detailed Setting.
2. Change Points to desired size. The point allocation from all areas must not exceed the Total Device size.
3. Click Apply.
4. Write to the PLC (Online \> Write to PLC) and initiate a power cycle.

### Using GX Works3 to Troubleshoot

If you have access to GX Works3, you can use the Device/Buffer Memory Batch Monitor feature to test or troubleshoot your connection. This can be found under Online \> Monitor \> Device/Buffer Memory Batch Monitor. Type in the device keyword with an offset and hit enter to begin monitoring values.

GX Works also has an Ethernet Diagnostics tool which is useful for determining the status of the connection as well as other information like IP Address, Port No, and Latest Error Code. To access this tool, navigate to Diagnostics \> Ethernet Diagnostics.

---

<div class="post-metadata">

**Author:** ![ggross](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ggross/32/12668_2.png) [@ggross](https://forum.inductiveautomation.com/u/ggross)\
**Post date:** [May 15, 2023, 6:03pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/2 "2023-05-15T18:03:51Z")

</div>

Pinned on May 15, 2023, 6:03pm UTC



---

<div class="post-metadata">

**Author:** ![Tom\_Gjonaj](https://avatars.discourse-cdn.com/v4/letter/t/779978/32.png) [@Tom\_Gjonaj](https://forum.inductiveautomation.com/u/Tom_Gjonaj)\
**Post date:** [June 1, 2023, 3:47pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/3 "2023-06-01T15:47:24Z")

</div>

This is great news and perfect timing. We are planning to implement a huge cell assembly line for our gigafactory and all of the machine's will be running Mitsubishi PLCs. If I can eliminate the need for kepware, that would be amazing.

---

<div class="post-metadata">

**Author:** ![Baskar\_Arumugam](https://avatars.discourse-cdn.com/v4/letter/b/94ad74/32.png) [@Baskar\_Arumugam](https://forum.inductiveautomation.com/u/Baskar_Arumugam)\
**Post date:** [June 14, 2023, 6:11am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/4 "2023-06-14T06:11:34Z")

</div>

I am trying to connect R series PLC. But the connection status showing as Idle. I don’t know what is the issue. Please guide me.

---

<div class="post-metadata">

**Author:** ![ggross](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ggross/32/12668_2.png) [@ggross](https://forum.inductiveautomation.com/u/ggross)\
**Post date:** [June 14, 2023, 4:33pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/5 "2023-06-14T16:33:23Z")

</div>

@Baskar_Arumugam,  
This is something we have recently noticed and will be fixing in an upcoming release. What is occurring is the driver doesn't have anything to subscribe to, so it is lazily connecting to the device itself (and therefore it is in an Idle state). If you create an OPC tag in Ignition, it will connect to the device.

We have also found that just saving the device a second time will also take it out of an Idle state if you don't want to create any tags. Any save at this point will flip flop the state between `Connected` and `Idle` though.

Garth

---

<div class="post-metadata">

**Author:** ![ggross](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ggross/32/12668_2.png) [@ggross](https://forum.inductiveautomation.com/u/ggross)\
**Post date:** [July 29, 2023, 5:45am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/6 "2023-07-29T05:45:26Z")

</div>

Updating this thread to note that as of 8.1.31 Ignition will support the FX3U hardware series via the FX3U-ENET module.

8.1.31 also adds support for a new **Wstring** data type which is an analog for the **String [Unicode]** data type that is present in GX Works.

---

<div class="post-metadata">

**Author:** ![Kumar\_Kaushal\_Ojha1](https://avatars.discourse-cdn.com/v4/letter/k/e274bd/32.png) [@Kumar\_Kaushal\_Ojha1](https://forum.inductiveautomation.com/u/Kumar_Kaushal_Ojha1)\
**Post date:** [August 3, 2024, 4:41am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/7 "2024-08-03T04:41:21Z")

</div>

hi,  
Please help me out in how to define the tags in ignition from Mitsubishi Fx3u enet.

| Data Type | Constant | Device | Address |
| --- | --- | --- | --- |
| INT | | D2 | %MW0.2 |
| BOOL | | D222.0 | %MX0.222.0 |
| ARRAY [0..7] OF INT | | D600 | %MW0.600 |

---

<div class="post-metadata">

**Author:** ![ggross](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ggross/32/12668_2.png) [@ggross](https://forum.inductiveautomation.com/u/ggross)\
**Post date:** [August 4, 2024, 6:49am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/8 "2024-08-04T06:49:43Z")

</div>

I think this is what you would be looking for:

 ![Definitions](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/7/872e3c1ddc3a7e500dbfa96f395975039ee432f5.png)

By default the `D` Area is assumed to be a integer, and by specifying the `.0` notation Ignition will automatically interpret the address as a Boolean.

The only one that should need explicit datatype handling is the array.

When importing from via the OPC Browser the tags look like the following:

 ![Results](https://us1.discourse-cdn.com/inductiveautomation/original/3X/f/a/fa897a5d315342f3fa9a460f9c5f3e10fa2e4bbc.png)

Garth

---

<div class="post-metadata">

**Author:** ![Kumar\_Kaushal\_Ojha1](https://avatars.discourse-cdn.com/v4/letter/k/e274bd/32.png) [@Kumar\_Kaushal\_Ojha1](https://forum.inductiveautomation.com/u/Kumar_Kaushal_Ojha1)\
**Post date:** [August 4, 2024, 7:15am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/9 "2024-08-04T07:15:53Z")

</div>

Thank you for the support, it’s working. Great work 👍

---

<div class="post-metadata">

**Author:** ![kavya\_shree](https://avatars.discourse-cdn.com/v4/letter/k/b4bc9f/32.png) [@kavya\_shree](https://forum.inductiveautomation.com/u/kavya_shree)\
**Post date:** [August 22, 2024, 10:54am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/10 "2024-08-22T10:54:47Z")

</div>

hi,  
Can please help me in how to get the value for float value same as how we got it for string.

---

<div class="post-metadata">

**Author:** ![Cody\_Morgan](https://avatars.discourse-cdn.com/v4/letter/c/db5fbb/32.png) [@Cody\_Morgan](https://forum.inductiveautomation.com/u/Cody_Morgan)\
**Post date:** [August 22, 2024, 2:38pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/11 "2024-08-22T14:38:20Z")

</div>

It's tough to say without knowing the data on your PLC, but you're probably looking for an address similar to: `D<Float>0` replacing 'D' with the area you want to read from and replacing '0' with the correct offset. This will read 4 bytes from the PLC to make a 32 bit floating point value. If you're looking for a 64 bit floating point value, use 'Double' instead of 'Float'.

Hope this helps!

---

<div class="post-metadata">

**Author:** ![Shashikant\_Jadhav](https://avatars.discourse-cdn.com/v4/letter/s/73ab20/32.png) [@Shashikant\_Jadhav](https://forum.inductiveautomation.com/u/Shashikant_Jadhav)\
**Post date:** [September 6, 2024, 4:36am UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/12 "2024-09-06T04:36:15Z")

</div>

This information really help us to connect Mitsubishi Q series CPU to ignition directly.

---

<div class="post-metadata">

**Author:** ![cugzhaolei](https://avatars.discourse-cdn.com/v4/letter/c/a4c791/32.png) [@cugzhaolei](https://forum.inductiveautomation.com/u/cugzhaolei)\
**Post date:** [July 8, 2025, 1:59pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/13 "2025-07-08T13:59:45Z")

</div>

hello, when will Ignition support Mitsubishi PLC data read from PLC tags? many plc engineers don't allocate soft unit addresses in GX3 Works. so ignition can't get data from PLC side, it's really a problem when we use ignition , thank you

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 8, 2025, 3:13pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/14 "2025-07-08T15:13:45Z")

</div>

Does Mitsubishi document a procedure for external systems to probe the PLC to determine what tags are at what addresses? (Presuming that information is actually presenting in the running PLC....)

Until Mitsu does that, Ignition simply won't be able to automatically use named tags. 🤷‍♂️

(This is one of the reasons Rockwell remains popular, in spite of its software miseries--Logix PLCs expose their tag names in a documented way.)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 8, 2025, 3:21pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/15 "2025-07-08T15:21:30Z")

</div>

I assume he's talking about Label access here.

AFAIK there is no way to interrogate/browse. There is a way to export label information from GX Works, though we had enough trouble with it during development we decided not to support it in the initial release and to revisit it later. Kepware doesn't/didn't support label access either, we figured there was probably a reason for it...

Also it seems to be for the iQ-R only (the label access commands in the MELSEC protocol, not necessarily the label concept).

---

<div class="post-metadata">

**Author:** ![cugzhaolei](https://avatars.discourse-cdn.com/v4/letter/c/a4c791/32.png) [@cugzhaolei](https://forum.inductiveautomation.com/u/cugzhaolei)\
**Post date:** [July 10, 2025, 2:11pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/16 "2025-07-10T14:11:22Z")

</div>

Good Morning,  
Thank you Kevin. I saw the Mitsubishi SLMP protocol official document which describes the they support access label via SLMP , as you can see from the document. and I know some software supports Mitsubishi PLC tag path read. So I think in technical side it can be read, and great engineers in your team can make it . 😀 👍

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/2/3/230c654e576537151e97df482c1db00b4827453e.png)

If you need more information, I can provide what I know to you. Thank you

And there also another problem when I use Mitsubishi PLC , the iQ-R series when I read a string array from PLC registers such as this path D\<string20[2]\>19420 , ignition will return error like this, is it because I used the wrong path? or wrong format ( when I use the same format to read int array, ignition will get the real data, so I don't know what's wrong with this, above address is D12003 -\> value is okay, below address is D\<string32[2]\>12091 -\> Error Configuration).

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/4/e4dd96e3fa9cc9c6b938a79d7f98184a77fa787b.png)

when I read the string from the start address like this  
D12091 ， it will work

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/3/8/3846d13661cd4f02114f18ad13038d49faeb69cb.png)

Have a nice day!!!!

---

<div class="post-metadata">

**Author:** ![cugzhaolei](https://avatars.discourse-cdn.com/v4/letter/c/a4c791/32.png) [@cugzhaolei](https://forum.inductiveautomation.com/u/cugzhaolei)\
**Post date:** [July 10, 2025, 2:16pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/17 "2025-07-10T14:16:53Z")

</div>

Hello Mr Pturmel,

Mr Kevin replied to my question. Thank you for your support.

I exported tag labels from Mitsubishi PLC from GX Works. The label always prefix GV:xxx like this

```python
              <data name="http://www.mitsubishielectric.com/xml/variableStructDeviceAssignment" handleUnknown="implementation">
                <variableStructDeviceAssignment>
                  <member name="xxxx" address="GV:3B4E4" />
                </variableStructDeviceAssignment>
              </data>

```

Hope ignition will support label reading in the future 👍

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 10, 2025, 2:17pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/18 "2025-07-10T14:17:53Z")

</div>

> [@cugzhaolei](#):
>
> And there also another problem when I use Mitsubishi PLC , the iQ-R series when I read a string array from PLC registers such as this path D\<string20[2]\>19420

String _arrays_ are not supported. You must address each string as its own tag, adjusting the offset as necessary.

---

<div class="post-metadata">

**Author:** ![cugzhaolei](https://avatars.discourse-cdn.com/v4/letter/c/a4c791/32.png) [@cugzhaolei](https://forum.inductiveautomation.com/u/cugzhaolei)\
**Post date:** [July 10, 2025, 3:19pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/19 "2025-07-10T15:19:55Z")

</div>

No problem, thank you Kevin 👍

---

<div class="post-metadata">

**Author:** ![diego120](https://avatars.discourse-cdn.com/v4/letter/d/ee59a6/32.png) [@diego120](https://forum.inductiveautomation.com/u/diego120)\
**Post date:** [July 31, 2026, 6:43pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/20 "2026-07-31T18:43:16Z")

</div>

Hello There!, Looking at the last answer i guess that for Latch Relay the arrays are not supported, right??