Arrays in the `L` device should work, it's just String datatypes that are a special case.

---

<div class="post-metadata">

**Author:** ![diego120](https://avatars.discourse-cdn.com/v4/letter/d/ee59a6/32.png) [@diego120](https://forum.inductiveautomation.com/u/diego120)\
**Post date:** [July 31, 2026, 10:08pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/22 "2026-07-31T22:08:46Z")

</div>

Am I using the correct structure??

I used 3 different structures, but the answer was the same,"quality: bad", i´m not sure the way i need to register this data type, here an example, i´m trying to read the values from L1801 to L1821

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/8/a/8aa4e07f33c1402ba03acb0d3f3bb54667d9ca26.png)

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [July 31, 2026, 10:15pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/23 "2026-07-31T22:15:43Z")

</div>

`L<bool[20]>1801` looks okay syntactically.

Find the logger(s) for `drivers.mitsubishi.Requests` and set them to DEBUG or TRACE and see if there's any relevant messages in the logs.

> **[Changing Logging Levels​ - Logs | Ignition User Manual](https://docs.inductiveautomation.com/docs/8.3/platform/gateway/web-interface/diagnostics/diagnostics-logs#changing-logging-levels)**
>
> One of the most important troubleshooting tools of the Gateway Webpage is the Logs page. This console shows errors caused by Gateway events like database or device connections, authentication profiles, Alarm Journals and pipelines, and anything else...

---

<div class="post-metadata">

**Author:** ![diego120](https://avatars.discourse-cdn.com/v4/letter/d/ee59a6/32.png) [@diego120](https://forum.inductiveautomation.com/u/diego120)\
**Post date:** [August 3, 2026, 5:30pm UTC](https://forum.inductiveautomation.com/t/mitsubishi-driver/73741/24 "2026-08-03T17:30:42Z")

</div>

![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/a/2/a20da489a31011cc0216e72899d113a655178753.png)

Yeah, I enabled Trace on drivers.mitsubishi.requests.

Reading L\<bool[50]\>1801 produces the answer from the screenshot,

Note it´s routed through BatchReadWordRequest- there doesn´t appear to be a BatchReadBitRequest logger. Sigle-bit reads (L1801) work fine and return good