@d.vasilev

netsh int tcp set global ecncapability=disabled

Thanks for the above command, this also solved my problem!  
Connected within 1 second, being connected for 16 minutes without drop-outs…

Man, unbelievable how much time I lost looking into this.  
Even our IT guys didn’t know much about that ECN capability on the server side…