# Modbus address problem

**URL:** <https://forum.inductiveautomation.com/t/modbus-address-problem/23976>\
**Category:** Ignition\
**Created:** [April 9, 2019, 10:09pm UTC](https://forum.inductiveautomation.com/t/modbus-address-problem/23976 "2019-04-09T22:09:35Z")\
**Posts on this page:** 2\
**Page:** 1

<div class="post-metadata">

**Author:** ![GeraGarcia](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/geragarcia/32/18471_2.png) [@GeraGarcia](https://forum.inductiveautomation.com/u/GeraGarcia)\
**Post date:** [April 9, 2019, 10:09pm UTC](https://forum.inductiveautomation.com/t/modbus-address-problem/23976/1 "2019-04-09T22:09:35Z")

</div>

Hi, i want to connect a modbus INTECONT SatusBelt Weigher from schenck Fig\_01.

the weigth instrument have a modbus TCP protocol, how you see into Fig\_02, y take the modbus address as show the fig\_03.

but i don’t have data has you see into the fig\_07 & fig\_08. i use the manual selection (HR) and the Choose OPC item, as you can see into fig\_04, fig\_05… fig\_08.

what i have wrong? to get the value from this modebus address.

Regards Gerardo Garcia

 ![Fig_01](https://us1.discourse-cdn.com/inductiveautomation/original/2X/1/181311e409c7b3b01bcecf4d62edeb55955ce5bf.jpeg) ![Fig_02](https://us1.discourse-cdn.com/inductiveautomation/original/2X/4/4ea40f2ec3ac7f1e903cace4d1594fdad1a3861b.png) ![Fig_03](https://us1.discourse-cdn.com/inductiveautomation/original/2X/0/0b578ed7790052b84585634f4b942ba176d5d614.png) ![Fig_04](https://us1.discourse-cdn.com/inductiveautomation/original/2X/8/80770b5e5fcf0a2ec7f1e67b967223825d9b2c48.png) ![Fig_05](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c253f70bc81c01493ba672a18e648c11675bba0c.png) ![Fig_06](https://us1.discourse-cdn.com/inductiveautomation/original/2X/c/c812e6e73143e87b7a90dfb1693a75edb9eedd31.png) ![Fig_07](https://us1.discourse-cdn.com/inductiveautomation/original/2X/9/951929ff90b4078cdfe77a51059195f27c9e8550.jpeg) ![Fig_08](https://us1.discourse-cdn.com/inductiveautomation/original/2X/5/51d6068a9a1db3785e158899198683c5c4c38121.jpeg)

for the actual value i use a 48, 048 & 0048 modbus address has you see into fig\_03, but dont work

---

<div class="post-metadata">

**Author:** ![GeraGarcia](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/geragarcia/32/18471_2.png) [@GeraGarcia](https://forum.inductiveautomation.com/u/GeraGarcia)\
**Post date:** [February 19, 2020, 4:53pm UTC](https://forum.inductiveautomation.com/t/modbus-address-problem/23976/2 "2020-02-19T16:53:31Z")

</div>

I can resolve this problem with:

1. from Fig\_.03, the address is 1873 with the modbus address adjust insted 48  
2.- configure true for Reverse Word Order and true for Reverse String Byte Order in Show advanced properties of OPC-UA Server-Devices