Hello all, I am trying to read the temo via modus from IDEC PLC.  
The HR registers are giving me data but its a multiplier of 10.

 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/e/ee9a96230ddc6de2fd083e45308612b3e0acfc34.png)  
The image shows 750 as the output but in reality it is 75.0F . How do I convert it ?  
 ![image](https://us1.discourse-cdn.com/inductiveautomation/original/3X/e/8/e88fb1efa5ebe5938b2d90a1484a9a13d5ddfd74.png)

---

<div class="post-metadata">

**Author:** ![Samuel\_Sueur](https://avatars.discourse-cdn.com/v4/letter/s/e36b37/32.png) [@Samuel\_Sueur](https://forum.inductiveautomation.com/u/Samuel_Sueur)\
**Post date:** [November 13, 2024, 8:47pm UTC](https://forum.inductiveautomation.com/t/modbus-conversion-decimal/98582/2 "2024-11-13T20:47:49Z")

</div>

Hi,

Use tag scaling.

> **[Tag Scaling Properties | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.1/platform/tags/tag-properties/tag-scaling-properties)**
>
> Configuring a Tag's scaling will condition the data for use within the Ignition Designer. Scaling will take the raw PLC value driving a Tag, do some math, and use the resulting value as the value of that Tag. Scaling works both ways. When you write...

For your use case, you need to set the following:

Scale mode: Linear  
Raw Low: 0  
Raw High: 100  
Scaled Low: 0  
Scaled High: 10

The default settings should be enough.