# Modbus import configuration

**URL:** <https://forum.inductiveautomation.com/t/modbus-import-configuration/9932>\
**Category:** General Discussion\
**Created:** [April 20, 2015, 1:47pm UTC](https://forum.inductiveautomation.com/t/modbus-import-configuration/9932 "2015-04-20T13:47:59Z")\
**Posts on this page:** 4\
**Page:** 1

<div class="post-metadata">

**Author:** ![efimov](https://avatars.discourse-cdn.com/v4/letter/e/ecccb3/32.png) [@efimov](https://forum.inductiveautomation.com/u/efimov)\
**Post date:** [April 20, 2015, 1:47pm UTC](https://forum.inductiveautomation.com/t/modbus-import-configuration/9932/1 "2015-04-20T13:47:59Z")

</div>

Hi guys,  
Some problem with import Address Mapping for modbus configuration.  
See please, what I’m doing wrong?  
[modbus-config.csv](https://us1.discourse-cdn.com/inductiveautomation/original/2X/d/d5e2a9acbc47fe90bd7348450d88e46ad2f04377.csv) (15.5 KB)

---

<div class="post-metadata">

**Author:** ![AlThePal](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/althepal/32/3603_2.png) [@AlThePal](https://forum.inductiveautomation.com/u/AlThePal)\
**Post date:** [April 23, 2015, 8:45am UTC](https://forum.inductiveautomation.com/t/modbus-import-configuration/9932/2 "2015-04-23T08:45:18Z")

</div>

Can you tell us what you think is wrong? I would suggest that the ‘Step’ value for each line is set to False as you’re only reading in one entry per line. Other than that it looks OK to me.

---

<div class="post-metadata">

**Author:** ![greg.simpson](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/greg.simpson/32/3135_2.png) [@greg.simpson](https://forum.inductiveautomation.com/u/greg.simpson)\
**Post date:** [April 27, 2015, 9:04pm UTC](https://forum.inductiveautomation.com/t/modbus-import-configuration/9932/3 "2015-04-27T21:04:16Z")

</div>

I agree, the CSV file looks correct. What problems are you having?

---

<div class="post-metadata">

**Author:** ![efimov](https://avatars.discourse-cdn.com/v4/letter/e/ecccb3/32.png) [@efimov](https://forum.inductiveautomation.com/u/efimov)\
**Post date:** [May 14, 2015, 3:51am UTC](https://forum.inductiveautomation.com/t/modbus-import-configuration/9932/4 "2015-05-14T03:51:48Z")

</div>

sorry for the silence. issue has been resolved, support answer:  
  
You should be able to import the file up to 286 rows long. You may need to create a second logical connection to the same device for additional rows.