# Modbus Poll Delay

**URL:** <https://forum.inductiveautomation.com/t/modbus-poll-delay/91393>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [June 5, 2024, 8:04am UTC](https://forum.inductiveautomation.com/t/modbus-poll-delay/91393 "2024-06-05T08:04:00Z")\
**Posts on this page:** 5\
**Page:** 1

<div class="post-metadata">

**Author:** ![nikunj.pipariya](https://avatars.discourse-cdn.com/v4/letter/n/cc9497/32.png) [@nikunj.pipariya](https://forum.inductiveautomation.com/u/nikunj.pipariya)\
**Post date:** [June 5, 2024, 8:04am UTC](https://forum.inductiveautomation.com/t/modbus-poll-delay/91393/1 "2024-06-05T08:04:00Z")

</div>

How to Set Poll Day Delay in Ignition, I see it shows only communication timeout in Modbus settings. Is there any backend setting available for this poll delay.

---

<div class="post-metadata">

**Author:** ![David\_Stone](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/david_stone/32/79749_2.png) [@David\_Stone](https://forum.inductiveautomation.com/u/David_Stone)\
**Post date:** [June 5, 2024, 11:37am UTC](https://forum.inductiveautomation.com/t/modbus-poll-delay/91393/2 "2024-06-05T11:37:22Z")

</div>

If you are after a setting to configure the poll rate for modbus tags, you would set up the individual tags in ignition then assign them to a Tag Group. The tag group specifies the rate that the Ignition gateway polls the tags for values.

> **[Tag Groups | Ignition User Manual](https://www.docs.inductiveautomation.com/docs/8.1/platform/tags/tag-groups)**
>
> What Is a Tag Group?

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [June 5, 2024, 11:48am UTC](https://forum.inductiveautomation.com/t/modbus-poll-delay/91393/3 "2024-06-05T11:48:07Z")

</div>

If you mean delays **between** commands, no, Ignition's Modbus driver doesn't have a setting for that. As it happens, my alternate driver **does** have this setting:

> [@Automation Professionals' Advanced Modbus Driver](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312):
>
> Automation Professionals is pleased to announce the first beta for its Advanced Modbus Driver, for Ignition version 7.9. Key features: Server mode, emulating one or more slave [devices](https://www.automation-pros.com/modbus/UserManual.pdf), using any of the three typical connection types, including simultaneous connections of multiple types. Client mode, incorporating all three connection modes in one driver. Support for Modbus Function Codes 20 and 21, File Records. Configure protocol tweaks for troublesome devices per slave unit, enabling suppor…

---

<div class="post-metadata">

**Author:** ![nikunj.pipariya](https://avatars.discourse-cdn.com/v4/letter/n/cc9497/32.png) [@nikunj.pipariya](https://forum.inductiveautomation.com/u/nikunj.pipariya)\
**Post date:** [June 5, 2024, 12:47pm UTC](https://forum.inductiveautomation.com/t/modbus-poll-delay/91393/4 "2024-06-05T12:47:19Z")

</div>

Thanks David, this should solve the problem..

---

<div class="post-metadata">

**Author:** ![nikunj.pipariya](https://avatars.discourse-cdn.com/v4/letter/n/cc9497/32.png) [@nikunj.pipariya](https://forum.inductiveautomation.com/u/nikunj.pipariya)\
**Post date:** [June 5, 2024, 12:50pm UTC](https://forum.inductiveautomation.com/t/modbus-poll-delay/91393/5 "2024-06-05T12:50:26Z")

</div>

> [@Automation Professionals' Advanced Modbus Driver](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/1):
>
> e first beta for its Advanced Modbus Driver, for Ignition version 7.9. Key features: Server mode, emulating one or more slave [devices](https://www.automation-pros.com/modbus/UserManual.pdf), using any of the three typical connection types, including simultaneous connection

-Hello, No I wanted to have poll delay for entire device only. Actually IFIX SCADA has this feature as well, to set poll delay for each register/register groups. With ignition same can be achieved as David\_Stone suggested.