You might get some ideas here:

> [@Modbus rtu over tcp read failure](http://forum.inductiveautomation.com/t/modbus-rtu-over-tcp-read-failure/35815/13):
>
> Your network load is not the problem. Based on your JSON export, most of your tags are contiguous, words 22-35, with three others: 6-7, 44-45, and 66-67. Ideally, you need four requests to read these blocks, satisfying the ten float tags. Per the modbus specification (PI-MBUS-300 from [modbus.org](http://modbus.org)) these requests and their responses should take 62.5ms at 19200-N-8-1 (including the inter-message silent time on the wire). Twenty devices is a modest overload–you won’t get one-second timing. I be…

---

_[View the full topic](https://forum.inductiveautomation.com/t/modbus-rtu-communication-time-out-faillure/41033)._