It already supports that, either via a gateway serial port, or via a remote ethernet-to-serial converter. I have clients using it specifically because it has sane multi-drop behaviors and very predictable slave interleaving. Perhaps you should try it?

See this comment and the question above it:

> [@Automation Professionals' Advanced Modbus Driver](https://forum.inductiveautomation.com/t/automation-professionals-advanced-modbus-driver/41312/164):
>
> There is no 1:1 equivalent. But the driver does round-robin scheduling of requests to units, and has per-unit rate limits. If, in a single poll rate, you have multiple requests to each of four units, they'll be executed like so: Unit 1 Req 1 Unit 2 Req 1 Unit 3 Req 1 Unit 4 Req 1 Unit 1 Req 2 Unit 2 Req 2 .... If the each set of requests takes longer than the per-unit rate limit, then the poll will smoothly run through all of the requests from start to finish, then wait for the next poll s…

---