# Modbus TCP communication with Viewmarq LED sign

**URL:** <https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146>\
**Category:** Ignition\
**Created:** [March 13, 2022, 5:05am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146 "2022-03-13T05:05:09Z")\
**Posts on this page:** 14\
**Page:** 1

<div class="post-metadata">

**Author:** ![NII](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nii/32/12920_2.png) [@NII](https://forum.inductiveautomation.com/u/NII)\
**Post date:** [March 13, 2022, 5:05am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/1 "2022-03-13T05:05:09Z")

</div>

Does anybody use a [Viewmarq](https://www.automationdirect.com/adc/shopping/catalog/hmi_(human_machine_interface)/viewmarq_led_message_displays/viewmarq_led_message_displays/md4-0124t) led sign by Automationdirect with Ignition?

I have no luck trying to connect it using modbus tcp.

---

<div class="post-metadata">

**Author:** ![josborn](https://avatars.discourse-cdn.com/v4/letter/j/4bbf92/32.png) [@josborn](https://forum.inductiveautomation.com/u/josborn)\
**Post date:** [March 14, 2022, 12:39am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/2 "2022-03-14T00:39:39Z")

</div>

I have not, but their documentation is quite thorough. Where are you stuck, do you have a valid OPC device connection? Or do you have a valid connection but cant successfully write to your display?

A quick skim of the manual and i think they by default use unit id 255, in which case you would need to include it in your ignition Modbus addressing. Something like `[deviceName]255.HRS11000`

If you have any errors or configs you can share that will help also.

---

<div class="post-metadata">

**Author:** ![NII](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nii/32/12920_2.png) [@NII](https://forum.inductiveautomation.com/u/NII)\
**Post date:** [March 14, 2022, 1:28am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/3 "2022-03-14T01:28:29Z")

</div>

I have a good connection but am not able to figure out how to write to it. In their documentation, this how to write:

> Blockquote  
> Command Strings are written to the ViewMarq Command String buffer starting at Modbus  
> Registers 411000 (up to 256 words).

I tried creating a tag [deviceName]1.HRUS11000 but when I insert a string it gives:  
 ![error](https://us1.discourse-cdn.com/inductiveautomation/original/3X/d/f/df43e227a6daf060c9b9bcb262c01a2d70a7faf7.jpeg)

It looks like I have to write each character in the string to each modbus registers starting at 411000, not sure if this is what it is expecting.

---

<div class="post-metadata">

**Author:** ![josborn](https://avatars.discourse-cdn.com/v4/letter/j/4bbf92/32.png) [@josborn](https://forum.inductiveautomation.com/u/josborn)\
**Post date:** [March 14, 2022, 1:52am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/4 "2022-03-14T01:52:00Z")

</div>

That’s a tag config error, try changing zero based addressing option. You will get that for lots of reasons, like typing in a bad scan class name, device name, or an address out of bounds. If your 1/0 starting is wrong you could be accessing 10999 instead of 11000.

---

<div class="post-metadata">

**Author:** ![Kevin.Herron](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/kevin.herron/32/7259_2.png) [@Kevin.Herron](https://forum.inductiveautomation.com/u/Kevin.Herron)\
**Post date:** [March 14, 2022, 2:59am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/5 "2022-03-14T02:59:41Z")

</div>

> [@NII](#):
>
> I tried creating a tag [deviceName]1.HRUS11000 but when I insert a string it gives:

`HRUS` and `HRS` are not the same type. Did you mean to address just a single unsigned register?

Also, when addressing a String (`HRS`), a length is required at the end.

[https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing](https://docs.inductiveautomation.com/display/DOC81/Modbus+Addressing)

---

<div class="post-metadata">

**Author:** ![josborn](https://avatars.discourse-cdn.com/v4/letter/j/4bbf92/32.png) [@josborn](https://forum.inductiveautomation.com/u/josborn)\
**Post date:** [March 14, 2022, 3:21am UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/6 "2022-03-14T03:21:04Z")

</div>

> [@Kevin.Herron](#):
>
> a length is required at the end

Thanks Kevin, i didnt know this, despite it being clearly stated in the manual as you indicated.

`HRS FORMAT: HRS<Modbus address>:<length>`

---

<div class="post-metadata">

**Author:** ![French\_Bolt](https://avatars.discourse-cdn.com/v4/letter/f/71e660/32.png) [@French\_Bolt](https://forum.inductiveautomation.com/u/French_Bolt)\
**Post date:** [March 9, 2023, 3:20pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/7 "2023-03-09T15:20:18Z")

</div>

I'm just checking to see if you were able to write to the Viewmarq. I too am struggling with this task. Looking to see how others have made this work.

---

<div class="post-metadata">

**Author:** ![NII](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nii/32/12920_2.png) [@NII](https://forum.inductiveautomation.com/u/NII)\
**Post date:** [March 9, 2023, 7:10pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/8 "2023-03-09T19:10:40Z")

</div>

What is the problem? What have you tried?

---

<div class="post-metadata">

**Author:** ![ryan.white](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/ryan.white/32/73193_2.png) [@ryan.white](https://forum.inductiveautomation.com/u/ryan.white)\
**Post date:** [March 9, 2023, 7:20pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/9 "2023-03-09T19:20:37Z")

</div>

For ours we have zero based addressing turned on and our tags are configured as `[deviceName]HRXXX`, no unit ID. Currently we are only writing integer values, we have not had a need to write strings to our displays yet.

---

<div class="post-metadata">

**Author:** ![French\_Bolt](https://avatars.discourse-cdn.com/v4/letter/f/71e660/32.png) [@French\_Bolt](https://forum.inductiveautomation.com/u/French_Bolt)\
**Post date:** [March 10, 2023, 12:53pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/10 "2023-03-10T12:53:40Z")

</div>

The messaging never gets to the marquee. "[RTE2\_T450\_Marquee]1.HRS200:20" without quotes. I don't know how to address the marquee properly, so this was my last attempt. The documentation is vague. Not sure what these values need to be or which ones are needed.

---

<div class="post-metadata">

**Author:** ![NII](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nii/32/12920_2.png) [@NII](https://forum.inductiveautomation.com/u/NII)\
**Post date:** [March 10, 2023, 4:24pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/11 "2023-03-10T16:24:13Z")

</div>

The code below works for me:

```auto
Msg = '<ID 0><CLR><WIN 0 0 287 31><POS 0 0><SL><S S><BL N><CS 0><GRN><T>Alarm >> </T><RED><STR 2 20>' + '\n'
system.opc.writeValues('Ignition OPC UA Server',['[ViewMarq]1.HRS11000:200'],[Msg])

```

HTH

---

<div class="post-metadata">

**Author:** ![French\_Bolt](https://avatars.discourse-cdn.com/v4/letter/f/71e660/32.png) [@French\_Bolt](https://forum.inductiveautomation.com/u/French_Bolt)\
**Post date:** [March 10, 2023, 5:12pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/12 "2023-03-10T17:12:51Z")

</div>

I will give this a shot. Regardless of the outcome, thank you for the assist.

---

<div class="post-metadata">

**Author:** ![French\_Bolt](https://avatars.discourse-cdn.com/v4/letter/f/71e660/32.png) [@French\_Bolt](https://forum.inductiveautomation.com/u/French_Bolt)\
**Post date:** [March 15, 2023, 12:19pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/13 "2023-03-15T12:19:30Z")

</div>

So I got my Click PLC talking to the marquee now. What I don't see is how to insert variables from the PLC into the marquee message. I have three numeric variables I need placed into the message, but I don't see a way to do that. Using Modbus TCP/IP.

---

<div class="post-metadata">

**Author:** ![NII](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/nii/32/12920_2.png) [@NII](https://forum.inductiveautomation.com/u/NII)\
**Post date:** [March 15, 2023, 6:13pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-communication-with-viewmarq-led-sign/57146/14 "2023-03-15T18:13:39Z")

</div>

Try:

```auto
var = 123
Msg = '<ID 1><CLR><WIN 0 0 287 31><POS 0 0><SL><S S><BL N><CS 0><GRN><T>' + str(var) + '</T><STR 1 20>' + '\r'	

```