# Modbus tcp device - adjust port for redundant gateway, or disable only some device in warm mode?

**URL:** <https://forum.inductiveautomation.com/t/modbus-tcp-device-adjust-port-for-redundant-gateway-or-disable-only-some-device-in-warm-mode/75856>\
**Category:** Ignition\
**Tags:** ignition81\
**Created:** [July 3, 2023, 3:48pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-device-adjust-port-for-redundant-gateway-or-disable-only-some-device-in-warm-mode/75856 "2023-07-03T15:48:23Z")\
**Posts on this page:** 3\
**Page:** 1

<div class="post-metadata">

**Author:** ![mazeyrat](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/mazeyrat/32/10955_2.png) [@mazeyrat](https://forum.inductiveautomation.com/u/mazeyrat)\
**Post date:** [July 3, 2023, 3:48pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-device-adjust-port-for-redundant-gateway-or-disable-only-some-device-in-warm-mode/75856/1 "2023-07-03T15:48:23Z")

</div>

@Kevin.Herron,

We have some modbus device that accept multiple TCP connection but only with different ports...  
8 simultaneous connection 502 to 510.

Siemens LOGO tiny PLC...  
 ![image](data:image/png;base64,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)

1. We would like to use our **redundant gateway in warm mode** but It's not possible to ajust another modbus port on the backup node ? Any workaround ? **Feature request...**

2. We could have our gateway in warm mode, and disable the warm mode for those device. **Feature request** : disable warm mode on a per device basis

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 3, 2023, 4:41pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-device-adjust-port-for-redundant-gateway-or-disable-only-some-device-in-warm-mode/75856/2 "2023-07-03T16:41:53Z")

</div>

Hmmm. That would be straight-forward to add to my driver...

---

<div class="post-metadata">

**Author:** ![pturmel](https://sea1.discourse-cdn.com/inductiveautomation/user_avatar/forum.inductiveautomation.com/pturmel/32/3295_2.png) [@pturmel](https://forum.inductiveautomation.com/u/pturmel)\
**Post date:** [July 3, 2023, 4:59pm UTC](https://forum.inductiveautomation.com/t/modbus-tcp-device-adjust-port-for-redundant-gateway-or-disable-only-some-device-in-warm-mode/75856/3 "2023-07-03T16:59:08Z")

</div>

That was easy:

[v1.1.2.231841656](https://www.automation-pros.com/ignition/Advanced%20Modbus%20Driver-1.1.2.231841656-v81.modl)

(In my driver, port number is specified with the hostname. With this change, you can set a completely different host or port for the backup server.)

My driver(s) treat warm as cold anyways, so it might have worked for you without this change.